Hi ,I have a wood cabin outside 70mtrs from house incoming supply, I was thinking of using a 35mm 2core pvc/swa, as I think a TT system would be appropriate for the cabin, owing to the distance away from house load would be allowing for diversity would be 51amps, seems a lot but it will be a live in dwelling with all requirements for cooking heating etc,am i correct with supply size Thanks ron
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
Advertisement - Content continues below

Strima

-
Arms
Esteemed
What's your installation method, earthing arrangement, bonding requirements?
 

Spoon

-
Mentor
Arms
Esteemed
Why not 25mm on 50A.
 
  • Thread Starter Thread Starter
  • #4
What's your installation method, earthing arrangement, bonding requirements?
Earthing wood be as TT supply, ie stake in the ground at hut position' bonding as regs, sub circuits would be 6242y and sized, appropriate for circuits suplied
 
  • Thread Starter Thread Starter
  • #5
Earthing wood be as TT supply, ie stake in the ground at hut position' bonding as regs, sub circuits would be 6242y and sized, appropriate for circuits suplied
PVC/SWA would be buried in the earth at appropriate at depth
 

telectrix

-
Mentor
Arms
Esteemed

telectrix

-
Mentor
Arms
Esteemed
soz. misread the table as 1.65mV
 
  • Thread Starter Thread Starter
  • #9
PVC/SWA would be buried in the earth at appropriate at depth
my calcs as follows , volt drop table 4E4B 1.85mv/a/mt 35mm =1.35 x50ampsx70mtrs =4.72 volts . 25mm = 1.85mv/a/mt x50amp x70mtr= 6.47volts so not much lighting load so 5% of 230volt=11.5volts allowed and 3% of 230volt =6.9 volts so would the calc with 5% be okay which is 11.5 volts am I getting to tied up ronky
 

Strima

-
Arms
Esteemed
Your volt drop needs to take into account the circuits within the cabin not just the distribution circuit.
 
T

Toneyz

Whilst cable size has been worked out to 25 or 35 due thought needs to be given to the terminal sizes and termination practicalities.
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to supply cable sizing in the Electrical Forum area at ElectriciansForums.net

Test Meter - Forum Sponsors since 2007!
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom