Hi guys I've attached a photo, at the roof of the bungalow (i've marked this in red) is where the SWA will come out of and down the wall, where it is marked in blue is the area I am concerned maybe 'at risk' from kicks and other problems from people walking past. The client has stated that the bit in blue that runs horizontally in front of the step will be concreted over once his outhouse has been completed.
What size galv conduit are you intending to use? 10mm2 2 core it will be a tight job to run that in conduit.
Pete999 - I'm going to spec the job again later today as things have changed somewhat from initially using 6mm to now using 10mm SWA, after reading everyone's advice I may leave out the galv conduit and run the cable clipped direct.
calculate VD for the sub first. from my previous post, for 6mm this would be 6V assuming a 40A load ( which is a bit pessimistic. then, calc. the shed VD.. add them together.
or just use some plastic duct. and i think 10mm is overkill.
I've calculated the Vdrop for the 10mm SWA on 40A MCB from the main board at 22m length run which comes to 3.8VD (1.68% of the allowable 5%)
The issue is the circuits coming off the sub-board.. for instance I've calculated the 2 double sockets that the client wants needs a run of 2.5 twin and earth on 32A MCB and 12m length run which comes to 5.76VD (2.5% of the allowable 5%)
IF i add these two figures together 1.68% and 2.5% i get 4.18% which is just below the allowable 5% (11.5V)
Am i right to add it like this and then do the same for the other circuits (lighting VD + 10mm SWA VD and air con VD + 10mm SWA) on the sub-board or should I treat them all individually and not add the figure for the VDrop figure for the 10mm SWA
personally, i add the voltages first, then work oyt the %. i'd not be too worried if the figure was over the 3% anyway. you got 10V to play with due to the silly 230V nominal voltage rubbish figure.
The total volt drop from the origin of the installation must not exceed 3% for lighting. For example if your distribution circuit is expected to carry a maximum load of 40a then the volt drop of both distribution circuit and the furthest point of the lighting circuit combined must not exceed 3%. Therefore you will calculate the maximum volt drop on your lighting circuit and add it to the calculated voltage drop on the sub. In total it should not exceed 6.9v
Put another way if your lighting circuit will have a VD of 2v from the CU then your distribution circuit fully loaded will have a permitted volt drop of 4.9v.