spud1

-
Arms
Hi,

Can anyone clarify for me the requirements regarding either the RCD protection of tails or glanding of tails entering a metal consumer unit in a TT system. With specific forethought to the upcoming amendment enforcing all metal consumer units.

Cheers
 
In the BYB:

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:

  • (i) have their enclosure manufactured from non-combustible material, or
  • (ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.
NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.
NOTE 2: The implementation date for this regulation is the 1st January 2016, but does not preclude compliance with the regulation prior to that date.

BTW, direct copy from the electronic version of the BYB a few seconds ago.
You know the scope of 61439-3
I realise that there are other 61439-* standards, and you could argue that some of them apply.
Also some similar switchgear will be made to alternative -* numbers, there in lies another failing of the reg.

So when has this changed? Where is the mention of 960° glow wire tested plastic not meeting this regulation?
 
So when has this changed? Where is the mention of 960° glow wire tested plastic not meeting this regulation?


You have been looking at the DPC.
This is from the released version.
The reference was removed between the DPC & the final draft for signing off, which I was lucky to see a page of @ Elex Sandown.
The above quote is the actual reg that has been published.

There are also further changes that have gone in under the radar as it were.
 
You have been looking at the DPC.
This is from the released version.
The reference was removed between the DPC & the final draft for signing off, which I was lucky to see a page of @ Elex Sandown.
The above quote is the actual reg that has been published.

There are also further changes that have gone in under the radar as it were.

So bollo*ks to it then. 960° glow wire tested plastic is non-combustible as defined in the product standard. The version of the BYB I was shown had this reference in it. It seems this has now disappeared.

Why are we now having this conversation??

We can give up talking altogether about metal boards in domestic finally!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Tails - metal board - TT system
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
45
Unsolved
--

Advert

Thread statistics

Created
spud1,
Last reply from
spud1,
Replies
45
Views
11,973

Advert

Back
Top