I th

ought it was the opposite supplementary bonding could be omitted if conditions were met and under 701.411.3.3 circuits had to have protection by RCD/RCBO.
For the purpose of an EICR a code 2 would be appropriate only if neither RCD protection or supplementary bonding were in place, if only the latter is present a code 3 is sufficient .
 
Last edited by a moderator:
Of course, RCD's & RCBO's are only reliable if tested quarterly many times I've gone to test an existing RCD/RCBO and it has failed to operate as it has stuck.
 
My understanding, is that installations which complied at the time of design/construction but do not comply with current editions do not require upgrading.
As such anything that complied at the time of design/construction should only warrant a code C3.
As RCD protection for sockets which would reasonably be expected to supply portable equipment used outdoors was a requirement of both the 15th and 16th editions, it is unlikely that an external non RCD protected socket complied.

In such a situation I would use code C2 for all instances where RCD protection is now required.
 