This has turned into a farce.
Firstly unless the original flat is ground floor a code 3 would be appropriate for lack of RCD protection to any circuit.... unless SB is not in place in bathrooms , that and lack of additional protection to sockets which may supply equipment outdoors would warrant a code 2.
The only issue here is that as a remedial measure the electrician has introduced another non-compliance, which should itself warrant a code 3.
It has been said that some would not even mention an up front 30ma RCD on an EICR. A recent ground floor flat that I tested had just that, and I gave it a code 2 as the flat was occupied by an elderly lady and the CU was out of reach at ceiling level.