A adam.h Oct 16, 2009 #1 What do you do about boiler timers, as wont they give false readings and will they not get damaged when doing an IR test? Do you have to remove them from the circuit?
What do you do about boiler timers, as wont they give false readings and will they not get damaged when doing an IR test? Do you have to remove them from the circuit?
Y Yooj Oct 16, 2009 #2 Either: Remove it. Isolate it if able to. There should be a fused spur feeding the boiler and associated switchgear (though make sure that it is osolated) Test with L&N together and E Test at 250V If you have GN3 look at section 2.7.7 (page 37), and also 612.3.2 of BS7671 Yooj Upvote 0
Either: Remove it. Isolate it if able to. There should be a fused spur feeding the boiler and associated switchgear (though make sure that it is osolated) Test with L&N together and E Test at 250V If you have GN3 look at section 2.7.7 (page 37), and also 612.3.2 of BS7671 Yooj