Hey guys I have my napit assesment in a couple of weeks just wanted some clarification on a few things. Firstly, when doing the efl test do I have to do it for each indervidual circuit or just for my ze then work out the zs by calculation? Secondly when doing the rcd test do I need to perform this for each circuit on the main rcd or just perform it for one circuit for each rcd eg downstairs sockets?sorry I'm just paincing a bit, I'm sure it will be fine. Thanks for your help guys.
 
Hi Bright spark you are correct in saying you'll be fine.Sounds to me like you know what your doing mate your just panicking. Done mine a few weeks ago guy was very nice. Just test aper normal you would test each circuit on a new installation. You would test Zs on each circuit you wouldnt normally do the calc. you might have show you know how to do the calc. But I am sure it will not be as intense as you think good luck mate
 
Thanks jmtisme, what questions where you asked? Also did you just do an rcd test for the two main rcds or perform the test on each individual circuit? Oh and finally one more question, did u fill in the test sheet before they arrived and just show them the results you found? Sorry.
 
RCD test is full test, x 1/2, x1, x5, both 0 & 180, don't forget to test the test button as well. 7 tests in all. once per RCD. not each cct. remember to test continuity on dead circiuts first. then Ze and Zs. be sure to know the relationship Zs+ Ze+ R1+R2 .
 
RCD test is full test, x 1/2, x1, x5, both 0 & 180, don't forget to test the test button as well. 7 tests in all. once per RCD. not each cct. remember to test continuity on dead circiuts first. then Ze and Zs. be sure to know the relationship Zs+ Ze+ R1+R2 .

A mistype there! Zs=Ze+(R1+R2)
 
I was asked aboit earthing systems. Zs r1+r2 had my test sheet filled out. then demonstrated to the guy what I did to get my results
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
testing for napit assesment!
Prefix
NAPIT Certification Scheme 
Forum
Certification NICEIC, NAPIT, Stroma, BECSA Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Bright.Spark,
Last reply from
jmtisme,
Replies
5
Views
3,270

Advert

Back
Top