Discuss Testing Help Please in the Canada area at ElectriciansForums.net
J
jordyboy004
been on the firm for nearlly 2 years now and ive never had to do a test and inspect on a property. well now the time has come and im not entirely sure what tests i need to do, could some please tell me if this is correct.
visual inspection
IR all the circuits
get a Z reading from all the circuits
RCD test
earth loop
pfc
any more?
thanks
you wana learn cris ban peef
continuity of bonding conductors and circuit protective conductors
continuity of ring final circuit
insulation resistance
barriers and enclosures
dead polarity (your doing this in ur continuity tests)(i think) or in the insulation R test
live polarity
Earth electrode ( zs )
earth fault loop impedance (ze )( zs)
PFC
funtional testing
hope that helps
yeah thats great thanks, the continuity ones i forgot. im just trying to make up a little help sheet for myself explaining how to do the tests, ive got a mind blank of the pfc one tho. am i right in thinking there is different ways to test this depending on the earthing system? hard to remember 3 years ago at college lol. oh and what is crisban peef lol
Jordyboy
PFC is made up of prospective earth fault current (PEFC) measured between phase (sorry Line now, i've got my 17th edition head on) and earth, and Prospective short ciruit current (PSCC) measured between line and neutral.
the highest of these two values gets entered on the paperwork against PFC
Correct order is
Continuity (Protective and bonding conductors)
Insualtion Resistance
Polarity (which ISNT part of the IR test Luke!!!!)
Earth Fault loop impedence (Ze, Zs and your PFC's)
RCD's
Be aware that the general conscensus on Zs measurements is now changing.
If you have Ze, and your (R1+R2) values then measuring Zs when you dont need to is in direct contravention of the Electricity at Work Regulations. :eek:
Generally, measure it at a socket with a plug in lead, and calculate everywhere else
I was taught the acronym
CRIPELR
Continuity
Ring continuity
Insulation resistance
Polarity
Electrode resistance
Loop impedance
Rcd
Reply to Testing Help Please in the Canada area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...