Discuss Testing RCBO at Light Switch in the ElectriciansForums.net News and Updates area at ElectriciansForums.net
Is it acceptable, using a two-wire RCBO tester, to test at a light switch using the phase and earth wires?
If it is acceptable are there any disadvantages?
it's acceptable, but RCBO should be tested at it's outgoing terminals with no load applied.that way, you are testing the RCD itself without any interference from the circuit.a ramp test could be erroneous if there are any loads with integral leakage on the circuit.
It could be a long night, and I haven't any pop corn. :)
We've had this debate many times before, and my recollection of the guidance given by manufactures, schemes and the like is vague, but I seem to recall it was split 50/50, with the other side of the debate stating it should be tested at a point on the circuit. Whilst the test is verify the function of the device, also it confirms its functioning with the circuit it has been connected to.
I agree with loads being disconnected, by the way.
Edit; GN3 isn't clear exactly, I believe? But this piece from the IET states 'Tests are made on the load side of the RCD between the line conductor of the protected circuit and the associated cpc. Any load or appliances should be disconnected prior to testing';
Inspection and testing of electrical installations: residual current devices - https://electrical.------.org/wiring-matters/issues/50/inspection-and-testing-of-electrical-installations-residual-current-devices/
I thought MW did a great job stating the situation, so I've a awarded a belated like, like.
He’s stated the situation, but not explained why he disagrees with Tel.
Does he disagree that it’s acceptable to test at the switch, or does he disagree that the test should be done at the terminals of the RCBO?
If I'm there to swop out a busted outlet I'd have to say I'm likely not isolating the whole installation to open the the board and remove conductors to test the RCD. Shall I get back on my horse and ride off?
Well, to my mind, if you’ve installed a socket which requires RCD protection, then you should be testing that the RCD provides protection to that socket.
Testing the RCD at it’s outgoing terminals doesn’t prove that the RCD will provide protection to the socket.
Telextric, as I understand it, you are saying that testing at the switch is acceptable but that testing at the outgoing terminals is preferable.
Do you think there is ever a case for using both methods?
I always test at the load side of the rcbo with finals disconnected but also like to test at the furthest point ,be that a socket or light etc.
Reply to Testing RCBO at Light Switch in the ElectriciansForums.net News and Updates area at ElectriciansForums.net
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Hi, I have a single light switch, wired like this.. the 2 wires in com, with a always live wire coming to the switch, and then wire going out to...
I own two flats with a small common lobby. Although operable from both flats, the common lobby light appears to be wired to flat A's circuit...
Hi, in my bedroom i had a 2 gang dimmer that powered 2 set of 3 spot lights and also had passthrough wires to other sockets. Im changing to just...