Hi guys,

Had Baxi round to do a service, and immediately after the central heating wasn’t turning on (hot water is fine).

Had them back out and they said the boiler is fine, it must be a faulty thermostat. Replaced the thermostat today, and still nothing.

When I connect the live and call wires in the thermostat, the boiler fires up and central heating goes on. However wired into thermostat (Drayton RTS1), I get nothing - not even a light on the thermostat.

Any idea what the cause might be here?

Thanks!
 
I suspect that the neutral to the thermostat has been disconnected.
Check you have 230v between live and N at the thermostat
 
I’ve just tested between live and neutral and it just zero?

Presumably it’s possible that said boiler service electrician disconnected the neutral?

Not sure what else could have stopped it working immediately afterwards?
 
That seems to confirm it, you have probably still got 230v on the live but no neutral
I would call the service guy Back and tell him to fix what he has broken.
 

Reply to Thermostat stopped clicking/no central heating in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
418
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
497
It has become a common occurrence that my boiler is failing to respond when the thermostat kicks in. I hear an audible click from the heatlink...
Replies
16
Views
2K
Hi everyone, my house has an air-to-heat system that generates hot water in a boiler. This boiler is then connected to the central heating...
Replies
1
Views
799
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
585

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock