S
sc_7901
hi there, I’m just looking for opinions/advice. A couple of years ago I had a 8.5kw Triton shower installed by a local company. In May it broke. Triton installed a 9.5kw omnicare. It’s broken again. Triton say the rcd is the issue this time. The RCD is 40 amp which apparently is not strong enough. What I find astounding is Triton did not check the rcd before installing the new unit. Apparently it’s not their job! Apparently the rcd wasn’t even right for the old 8.5kw shower either. Am I wrong for thinking Triton should’ve checked the electrics before installing the new one? I know they couldn’t have fixed it but I’d rather they had done that than leave me with a broken shower after 2 months!
they are talking out their corporate arses. 9.5kW = 40A, so the 40A RCD , although on it's limit, will not cause your problem.
My other half has informed me although the rcd is 40 the circuit breaker is 32. Would that be the issue?
a 32A breaker will trip at 40A in approx 10 minutes. that may be your cause.
What is good practice? Should Triton at least have had a look before installing the 9.5kw unit? Seems crazy that they wouldn’t, regardless of the fact they couldn’t rectify it.
If the rcd is tripping best you get the circuit and the shower tested .... .
Probably cost you about £50
Then you will know where the problem is
Did they carry out any form of testing when they swapped your shower and more importantly did they leave any certification?
TBH I know the answer already...
As far as I could tell, the only testing was switching it on. I wasn’t given any paperwork
Would the original installers, the local company who installed the 8.5kw, be liable since apparently they’ve installed the wrong rcd to begin with?