hi there, I’m just looking for opinions/advice. A couple of years ago I had a 8.5kw Triton shower installed by a local company. In May it broke. Triton installed a 9.5kw omnicare. It’s broken again. Triton say the rcd is the issue this time. The RCD is 40 amp which apparently is not strong enough. What I find astounding is Triton did not check the rcd before installing the new unit. Apparently it’s not their job! Apparently the rcd wasn’t even right for the old 8.5kw shower either. Am I wrong for thinking Triton should’ve checked the electrics before installing the new one? I know they couldn’t have fixed it but I’d rather they had done that than leave me with a broken shower after 2 months!
 
they are talking out their corporate arses. 9.5kW = 40A, so the 40A RCD , although on it's limit, will not cause your problem.
 
My other half has informed me although the rcd is 40 the circuit breaker is 32. Would that be the issue?
 
a 32A breaker will trip at 40A in approx 10 minutes. that may be your cause.
 
  • Agree
Reactions: EbolaSideRoom
What is good practice? Should Triton at least have had a look before installing the 9.5kw unit? Seems crazy that they wouldn’t, regardless of the fact they couldn’t rectify it.
 
If the rcd is tripping best you get the circuit and the shower tested .... .

Probably cost you about £50

Then you will know where the problem is
 
  • Like
Reactions: marconi and DPG
Did they carry out any form of testing when they swapped your shower and more importantly did they leave any certification?

TBH I know the answer already...
 
  • Like
Reactions: Rpa07 and DPG
Did they carry out any form of testing when they swapped your shower and more importantly did they leave any certification?

TBH I know the answer already...
As far as I could tell, the only testing was switching it on. I wasn’t given any paperwork
 
If the rcd is tripping best you get the circuit and the shower tested .... .

Probably cost you about £50

Then you will know where the problem is
Would the original installers, the local company who installed the 8.5kw, be liable since apparently they’ve installed the wrong rcd to begin with?
 
  • Disagree
Reactions: 1 person
Not taking the rise Mate, what else doesn't work when the Shower trips? is your fuseboard a modern one with 2 RCDs or just 1?
 
It’s just the shower that goes. That’s about as much as I can tell you. Sorry. Am clueless about this stuff. Looks as though the board was put in in 2010
 
It’s just the shower that goes. That’s about as much as I can tell you. Sorry. Am clueless about this stuff. Looks as though the board was put in in 2010
Without being there it's difficult to address the problem, but usually the RCD will be connected in conjunction with a number of MCBs, but you say it's only the shower that doesn't work, this makes me think it's the MCB that is tripping not the RCD, can you post what is written on the device that trips? Or better still a picture of the Consumers Unit (fuseboard) showing the item that trips.
 
  • Like
  • Agree
Reactions: telectrix and DPG
Hope these help!? On the bottom picture, “shower” is to the left of “lights”
758FD441-4F04-41CB-9281-EBCD87D4F978.jpeg
AC4D85B0-3992-4C63-A4C4-A94419B4822E.jpeg
 
Looks like a standalone RCD feeding the shower, can#t see how it will be a load issue, more likely a fault in the shower wiring or the shower, you will nee to get the wiring and shower tested by a skilled electrician, with the correct test gear.
 
Thanks. The guy from Triton is insisting no issues with the shower cos the guy checked the wiring. Sparky it is then!
 
  • Winner
Reactions: marconi

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Triton shower rcd issues
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
sc_7901,
Last reply from
Octopus,
Replies
28
Views
4,335

Advert