It’s just the shower that goes. That’s about as much as I can tell you. Sorry. Am clueless about this stuff. Looks as though the board was put in in 2010
 
It’s just the shower that goes. That’s about as much as I can tell you. Sorry. Am clueless about this stuff. Looks as though the board was put in in 2010
Without being there it's difficult to address the problem, but usually the RCD will be connected in conjunction with a number of MCBs, but you say it's only the shower that doesn't work, this makes me think it's the MCB that is tripping not the RCD, can you post what is written on the device that trips? Or better still a picture of the Consumers Unit (fuseboard) showing the item that trips.
 
Hope these help!? On the bottom picture, “shower” is to the left of “lights”
758FD441-4F04-41CB-9281-EBCD87D4F978.jpeg
AC4D85B0-3992-4C63-A4C4-A94419B4822E.jpeg
 
Looks like a standalone RCD feeding the shower, can#t see how it will be a load issue, more likely a fault in the shower wiring or the shower, you will nee to get the wiring and shower tested by a skilled electrician, with the correct test gear.
 
Thanks. The guy from Triton is insisting no issues with the shower cos the guy checked the wiring. Sparky it is then!
 
Thanks. The guy from Triton is insisting no issues with the shower cos the guy checked the wiring. Sparky it is then!
No certificates then, how or what did the shower guy do to check the wiring?
 
Just took the cover off the shower. Was a “visual inspection”. He certainly didn’t seem to have any kit with him
 
Just took the cover off the shower. Was a “visual inspection”. He certainly didn’t seem to have any kit with him
That figures, after the Sparks has done what he can, please let the forum know what transpired
 
Just took the cover off the shower. Was a “visual inspection”. He certainly didn’t seem to have any kit with him

Standard triton stuff, did a new install triton shower failed after a couple of months. Customer calls me I go out check it and test it all again everything fine told them to call triton. I wasnt there but apparently they turned up were there for about a minute didn’t take cover off and said you need to call your electrician back to do a ramp test on the rcd as that’s the problem, it wasn’t even tripping anything just cutting out. After telling the customer the circuit has been tested twice and is fine. I called triton myself got an engineer and met him on site who said the pcb has gone and the details he got from the previous engineer visit was that he didn’t have the right parts to fix it. Shower of ---- I’d say
 
Rant alert - the original service guy lied and his actions have caused increased costs for the Customer, You and his company. And he has brought his company into disrepute. I don't understand how service departments can tolerate this?
 
I got a sparky out. He put in a 45amp mcb so all seems fine now. I just feel like Triton could’ve handled it a lot better. I find it astounding that they would install a shower without at least looking at your electrics!
 
I got a sparky out. He put in a 45amp mcb so all seems fine now. I just feel like Triton could’ve handled it a lot better. I find it astounding that they would install a shower without at least looking at your electrics!
It's quite simple really Mate, the money they make from, say, selling 10 showers far outweighs the chances of 1 or 2 causing trouble for their customers.
 
I got a sparky out. He put in a 45amp mcb so all seems fine now. I just feel like Triton could’ve handled it a lot better. I find it astounding that they would install a shower without at least looking at your electrics!

Did he test the circuit and what does the certificate state?
 