S

sc_7901

hi there, I’m just looking for opinions/advice. A couple of years ago I had a 8.5kw Triton shower installed by a local company. In May it broke. Triton installed a 9.5kw omnicare. It’s broken again. Triton say the rcd is the issue this time. The RCD is 40 amp which apparently is not strong enough. What I find astounding is Triton did not check the rcd before installing the new unit. Apparently it’s not their job! Apparently the rcd wasn’t even right for the old 8.5kw shower either. Am I wrong for thinking Triton should’ve checked the electrics before installing the new one? I know they couldn’t have fixed it but I’d rather they had done that than leave me with a broken shower after 2 months!
 
they are talking out their corporate arses. 9.5kW = 40A, so the 40A RCD , although on it's limit, will not cause your problem.
 
My other half has informed me although the rcd is 40 the circuit breaker is 32. Would that be the issue?
 
a 32A breaker will trip at 40A in approx 10 minutes. that may be your cause.
 
  • Agree
Reactions: EbolaSideRoom
What is good practice? Should Triton at least have had a look before installing the 9.5kw unit? Seems crazy that they wouldn’t, regardless of the fact they couldn’t rectify it.
 
If the rcd is tripping best you get the circuit and the shower tested .... .

Probably cost you about £50

Then you will know where the problem is
 
  • Like
Reactions: marconi and DPG
Did they carry out any form of testing when they swapped your shower and more importantly did they leave any certification?

TBH I know the answer already...
 
  • Like
Reactions: Rpa07 and DPG
Did they carry out any form of testing when they swapped your shower and more importantly did they leave any certification?

TBH I know the answer already...
As far as I could tell, the only testing was switching it on. I wasn’t given any paperwork
 
If the rcd is tripping best you get the circuit and the shower tested .... .

Probably cost you about £50

Then you will know where the problem is
Would the original installers, the local company who installed the 8.5kw, be liable since apparently they’ve installed the wrong rcd to begin with?
 
  • Disagree
Reactions: 1 person
Not taking the rise Mate, what else doesn't work when the Shower trips? is your fuseboard a modern one with 2 RCDs or just 1?
 
It’s just the shower that goes. That’s about as much as I can tell you. Sorry. Am clueless about this stuff. Looks as though the board was put in in 2010
 
It’s just the shower that goes. That’s about as much as I can tell you. Sorry. Am clueless about this stuff. Looks as though the board was put in in 2010
Without being there it's difficult to address the problem, but usually the RCD will be connected in conjunction with a number of MCBs, but you say it's only the shower that doesn't work, this makes me think it's the MCB that is tripping not the RCD, can you post what is written on the device that trips? Or better still a picture of the Consumers Unit (fuseboard) showing the item that trips.
 
  • Like
  • Agree
Reactions: telectrix and DPG
Hope these help!? On the bottom picture, “shower” is to the left of “lights”
758FD441-4F04-41CB-9281-EBCD87D4F978.jpeg
AC4D85B0-3992-4C63-A4C4-A94419B4822E.jpeg
 
Looks like a standalone RCD feeding the shower, can#t see how it will be a load issue, more likely a fault in the shower wiring or the shower, you will nee to get the wiring and shower tested by a skilled electrician, with the correct test gear.
 
Thanks. The guy from Triton is insisting no issues with the shower cos the guy checked the wiring. Sparky it is then!
 
  • Winner
Reactions: marconi
Thanks. The guy from Triton is insisting no issues with the shower cos the guy checked the wiring. Sparky it is then!
No certificates then, how or what did the shower guy do to check the wiring?
 
Just took the cover off the shower. Was a “visual inspection”. He certainly didn’t seem to have any kit with him
 
  • Informative
Reactions: 1 person
Just took the cover off the shower. Was a “visual inspection”. He certainly didn’t seem to have any kit with him
That figures, after the Sparks has done what he can, please let the forum know what transpired
 
Just took the cover off the shower. Was a “visual inspection”. He certainly didn’t seem to have any kit with him

Standard triton stuff, did a new install triton shower failed after a couple of months. Customer calls me I go out check it and test it all again everything fine told them to call triton. I wasnt there but apparently they turned up were there for about a minute didn’t take cover off and said you need to call your electrician back to do a ramp test on the rcd as that’s the problem, it wasn’t even tripping anything just cutting out. After telling the customer the circuit has been tested twice and is fine. I called triton myself got an engineer and met him on site who said the pcb has gone and the details he got from the previous engineer visit was that he didn’t have the right parts to fix it. Shower of ---- I’d say
 
Rant alert - the original service guy lied and his actions have caused increased costs for the Customer, You and his company. And he has brought his company into disrepute. I don't understand how service departments can tolerate this?
 
I got a sparky out. He put in a 45amp mcb so all seems fine now. I just feel like Triton could’ve handled it a lot better. I find it astounding that they would install a shower without at least looking at your electrics!
 
  • Like
Reactions: DPG
I got a sparky out. He put in a 45amp mcb so all seems fine now. I just feel like Triton could’ve handled it a lot better. I find it astounding that they would install a shower without at least looking at your electrics!
It's quite simple really Mate, the money they make from, say, selling 10 showers far outweighs the chances of 1 or 2 causing trouble for their customers.
 
  • Like
Reactions: DPG
I got a sparky out. He put in a 45amp mcb so all seems fine now. I just feel like Triton could’ve handled it a lot better. I find it astounding that they would install a shower without at least looking at your electrics!

Did he test the circuit and what does the certificate state?
 
  • Optimistic
Reactions: DPG and Pete999

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Triton shower rcd issues
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
sc_7901,
Last reply from
Octopus,
Replies
28
Views
4,334

Advert