Yes forget the lightning rod bit it was just another thing on my mind, and yes i do bond the gas and water, When i did my electrical training (quite a few years ago now) i can remember someone asking about caravan points have to have its own earth rod and i asked why it couldnt have both earthing systems and he said about a fault from the TNCS system has the potential to go through the caravan and into the earth rod. Myself i think the more means of earthing a system getting the resistance down as low as possible has got to be a good thing.
Also a electrician i do alot of work with has just done the car charging point course that was an NICEIC one and he had said that all buildings not connected to the main house has GOT to have an earth rod for its earthing and must not use the pme earth, when the tutor was questioned about it by sparks on the course he said it seems a thing where older electricians use a rod while the newer trained ones do it wrong and use the TNCS house earth. Also regarding the water bond i have had people tell me if the water is in plastic pipe then you need to cut some copper into it so you can bond it, but it states in the OSG that if its plastic pipe then it dosent require bonding.
A test to verify if it is extraneous or not should be carried out to confirm if bonding is or is not required. Again GN8 explains this.