Yup very true, can't agree more.Compared to the **** that's going on in places like Syria I don't think any of us has got much to get arsey about. Especially stuff wrote on forums. Lol
Yup very true, can't agree more.Compared to the **** that's going on in places like Syria I don't think any of us has got much to get arsey about. Especially stuff wrote on forums. Lol
Thanks for your replies, its been driving me mad trying to find it written down anywhere, i also had a nic electrician telling me the other day he was told he had to do an earth bond to a lightning condutor on a house which i feel isnt right, if it did get struck by lightning then that could then travel through all the earthing into the house, and unless i am wrong i think a lightning conductor is sort of like a TT rod and you are told never to combine TNCS PME earthing to a TT system with a connecting earth!
Where are you getting this nonsense from?
Lightning conductors are an ECP and should be connected to the MET by a main bond.
Adding earth rods with a good Ra to the origin of a PME installation is a very good idea.
Lightning protection systems will be bonded to all exposed metalwork outside and the structural metalwork of the building, this will extend into the equipotential zone of the installation.
You will rarely see the main bond to a lightning protection system, the correct place to connect the bond is below ground level, often connected to the earth rod nearest the MET.
Lightning protection systems will be bonded to all exposed metalwork outside and the structural metalwork of the building, this will extend into the equipotential zone of the installation.
You will rarely see the main bond to a lightning protection system, the correct place to connect the bond is below ground level, often connected to the earth rod nearest the MET.
Lightning Protection systems should ''Always'' be bonded to the buildings MET, and as stated the connection is generally to the nearest down conductor earth rod, or in the case of a buried copper tape ring, to the nearest point on the copper tape!!
Neither of which explains the point of bonding a lightning conductor.....yes possibly if the LC is in contact with sructural steel,but more often than not the LC's I come across could not possibly introduce an earth potential into the equipotential zone.
I went to quote for a domestic after a lightning strike.
I was astounded by the damage.
The pole mounted TX was in bits all over the place.
The metal clad CU was blown to bits.
The internal fabric of the building had been destroyed by cables flapping about and bits of the roof were missing.
It was a bit unusual though.
The DNO guy attending afterwards said he'd been to loads of lightning strikes but never seen anything like it.
I got a couple of calls after the event from folks wanting lightning protection![]()
What sort of buildings with LP systems do you work on?? You'd be surprised what a few million volts can penetrate to get to earthed metalwork inside the building or structure or even metalwork that forms part of the buildings fabric (eg.. concrete rebar/reinforcement etc)
Compared to the **** that's going on in places like Syria I don't think any of us has got much to get arsey about. Especially stuff wrote on forums. Lol
Last EICR was a medieval stone build church with no other services requiring bonding....but also schools with LC provision. I have not seen any evidence of main bonding to the LC in any of the schools I work,but that does not mean it is not present. I remain unsure of this, there is a requirement to bond CH pipes,but I would only do so if those pipes were introducing an external earth potential to the equipotential zone,which is a rare scenario. Same for an LC entirely on the outside of the building. If that LC is attached to structural steel then it would be the steel i was looking to be bonded,not the LC.
Last EICR was a medieval stone build church with no other services requiring bonding....but also schools with LC provision. I have not seen any evidence of main bonding to the LC in any of the schools I work,but that does not mean it is not present. I remain unsure of this, there is a requirement to bond CH pipes,but I would only do so if those pipes were introducing an external earth potential to the equipotential zone,which is a rare scenario. Same for an LC entirely on the outside of the building. If that LC is attached to structural steel then it would be the steel i was looking to be bonded,not the LC.