JONNY BRIGGS

Hi guys, i have just installed a new rcd board into a house with a tt system.

When i turned the main switch on im not getting any voltage. The main switch is a bs842 chilton 100a type D earth leakage circuit breaker. This is the first tt system i have came across as im new to the industry and dont know how to fix the fault.

I have tested the switch and there is voltage going in but not out.

Any help would be amazing.

Cheers
 
That's a VOELCB, (with a Yellow test button) they are old voltage operated breakers and should be taken out of service as an earth leakage breaker as they are now obsolete!!

If you remove the earth conductors from this unit it can remain in circuit as a main isolator... Or, better still being a TT system, replace with a 100mA S type RCD, Giving enhanced/additional protection to the RCD CU you have just installed!!
 
Last edited by a moderator:
Agree with E54, nothing wrong with using it as an isolator only, but don't consider it for anything else, it sounds as though it is faulty though and needs removing if there is no power coming out of it.
 
I removed the earth conductors and im now getting voltage but no power throughout the house.

Any suggestions guys? Should i remove the main switch and put a new on in? Or just run the tails straight into the meter?

Cheers
 
Agree with E54, nothing wrong with using it as an isolator only, but don't consider it for anything else, it sounds as though it is faulty though and needs removing if there is no power coming out of it.

More than likely, that's the protective mechanism holding it open!!

Or maybe not!! From what you saying above. ...lol!!

Remove it and replace with a 100mA S Type RCD!!

BTW, ...what is your Ra value from the TT rod(s)??
 
Last edited by a moderator:
I removed the earth conductors and im now getting voltage but no power throughout the house.

Any suggestions guys? Should i remove the main switch and put a new on in? Or just run the tails straight into the meter?

Cheers

Don't understand how you can be getting "voltage" but no power. Are all devices closed?
 
I removed the earth conductors and im now getting voltage but no power throughout the house.

Any suggestions guys? Should i remove the main switch and put a new on in? Or just run the tails straight into the meter?

Cheers

Not sure I'd be meddling with the meter tails! lol
 