Assuming a TT with a stable low Ra. It would be possible to rely on fuses or mcb's for earth fault protection. Or would it? Why don't SP overcurrent devices have manufacturers instructions that they are not suitable for TT systems as apparently do some SP RCBO's?

Hi

Well they are okay, you just also need to have double pole isolation.

Cheers
 
I can't find any specific answer to this!

Here's another suggestion though, funnily enough in response to a question from yourself:)
See​
post #26
​
http://www.electriciansforums.co.uk...es-electrical-regulations/64662-rcbo-s-2.html

Hi

The answer has been given. On a TT system the Neutral isn't reliably earthed. So if we have a fault, phase to earth, could be a network fault or a property with no RCD, some of the voltage will be dropped accross the Transformer earth Rb, this raises the neutral Voltage. Any other system connected to that neutral will also see the Voltage, which can be considerable. So in a TT you need to isolate both poles.

Cheers
 