Discuss Twin and earth used as meter tails in the UK Electrical Forum area at ElectriciansForums.net
So i went to a job and i came across this the house is 19yrs old and apparently this is how it was when they moved in from when it was built its the twin and earth that runs to the consumer unit I am looking at there is some 10mm earth to the gas meter that has been fitted at a later date.20200613_145949.jpg
Yes, it is quite common (as far as houses that have longer than usual tails that is) but not something I would say is good practice due to the usual lack of physical protection along the sort of route often taken.
The meter is only2mts from it I am going to drop some 16mm earth from the consumer unit to the met
Why are you going to install a 16mm earth?
[automerge]1592079514[/automerge]
I thought I read that if it's a longer run your supposed to use SWA?
Nope, there is nothing that stipulates cables over any particular length need to be SWA.
Meter tails cannot be longer then 3m so a distribution circuit must be installed if the CU is further than this.
[automerge]1592079604[/automerge]
Just wondering if anyone else had seen any thing like it
Yes, lots of times, the exposed insulation is not acceptable but other than that if it is of suitable size and less than 3m it complies.
Can’t remember the table number off the top of me head mate but it’s in 7671 for main earth sizing or as above use the adibatic....I’d go with 7671 for design selection but do the adibatic if unsure of someone else’s work ?.......
Hi the 16mm earth is that not the std main earth size from a consumer unit to the DNO MET forgive me if i am wrong
For a new installation yes that is standard but for an existing installation you need to assess the suitablity of what is already installed.
Only a cowboy would charge a customer for an 'upgrade' when the existing installation is not unsafe.
[automerge]1592088004[/automerge]
Hi Mate am i a correct thinking that a 16mm earth is correct i just can not see that the cpc in a bit of twin and earth is adequate
Have you carried out the calculation using the adiabatic equation in BS7671?
Generally speaking the 6mm earthing conductor you have is more than adequate as long as it does not need to perform the function of a main bond (which it doesn't appear to here since the bonding connects directly to the cutout)
Hi Dave can i point out that i would not charge the people for a bit is cable that is in the van and 10mins of my time as i was there doing something else its not about charging someone
Ah, so it's a free of charge, potentially unnecessary upgrade?
So you can tell the customer that you have given them a free upgrade thus improving their safety when in reality you have potentially done unnecessary work.
Reply to Twin and earth used as meter tails in the UK Electrical Forum area at ElectriciansForums.net
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
hi....im running cable for a split type 1.5 hp aircon....i have a roll of english 2.5 twin & earth, is this ok for the job? im running it to the...
