I'm planning to get two single ovens and have been trying to find the best way to do the circuits. People seem to do it every way possible but I have doubts about some of the ways that they are done. The ovens I'm looking at are 16A appliances (max power is approx 14A), so I won't be plugging them into a socket.

My feeling is that two 16A radials would be best. Also, if one of the breakers trip then the other oven can still be used. The circuit(s) will be new so running two cables won't cost much more than one cable.

However, I hear about using a 32A breaker with a dual cooker connection unit and have seen this in people's homes. This seems to be the standard way of doing this but I can't understand how it's safe. There could be something simple that I'm missing though. The ovens (Bosch/NEF/Siemens) come with their own cable cable, and surely this cable would only be rated at 16A? If these cables have a 16A capacity and they go on a 32A breaker then surely that means that they aren't adequately protected? Is this really a safe (and regs compliant) way of doing it?

I think I know what is best but it really bugs me when I don't understand things. Equally, if my ovens were wired with a 32A breaker then I would worry about them unless somebody can explain how the cable won't go :fire: if there is a fault.
 
the ovens are fixed loads, i.e they can't overload the cables, so overcurrent protection is not required. short circuit protection is provided by a 32A breaker, however, so it complies.
 
Either or for me, depends if it’s an existing kitchen or it’s being extensively refurbished.

New circuits will require notification to local building control, if your feeling honest, or using a Scheme registered sparks.

This kitchen seems to be taking a long time, thought you would have it done for Xmas. :)
 
Hi - Probably a million homes have a single circuit with 32A MCB installed for cooking. But you can have as many circuits as you feel like, of course.
There are some domestic cookers now that have very high power requirements and thinking about those beasts it may give reason to have one of the cables in 10mm. Much more fun :) .
 
Either or for me, depends if it’s an existing kitchen or it’s being extensively refurbished.

New circuits will require notification to local building control, if your feeling honest, or using a Scheme registered sparks.

This kitchen seems to be taking a long time, thought you would have it done for Xmas. :)

Big refurb for me, so I think I'm decided on two circuits now as the cost difference is insignificant.

I should have it done for Xmas, just not this Xmas :). I've been doing other rooms, and almost ready for the kitchen now.
 
future proof it. `16mm SWA cleated along the worktop.:eek:

:laughing: I did consider 10mm for future proofing but I suspect it wouldn't go down the wall. 6mm will go down the wall quite easily but 10mm could turn into a much bigger job. I decided that I shouldn't be changing the kitchen for many years so I won't worry about the future too much. Two 16A radials (with the option of 20A breakers) + 32A for the Hob is still better than what most homes have.
 
is that 14A for each oven after diversity or that is the peak demand? You might find it is fine with both on a 16A supply with 2.5mm or maybe even 1.5mm cable depending on installation method etc.
 
is that 14A for each oven after diversity or that is the peak demand? You might find it is fine with both on a 16A supply with 2.5mm or maybe even 1.5mm cable depending on installation method etc.

14A is from the spec sheet (max load without diversity). I can't remember the exact numbers, they were 3000-4000W.
 
14A is from the spec sheet (max load without diversity). I can't remember the exact numbers, they were 3000-4000W.
well I'm no electrician, but in that case the design current could be 14.2A which would be 1.5mm cable in most circumstances and the breaker could be 16A. There's no penalty for using a larger cable though, other than cost, and ease of installation. I would still recommend hard wired on a separate circuit though, as plugging two ovens into the socket circuit would take up a lot of the capacity.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Berkshire

Thread Information

Title
Two ovens - how many circuits?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
23

Thread Tags

Advert

Thread statistics

Created
WiringPeter,
Last reply from
chrisdungan,
Replies
23
Views
12,137

Advert

Back
Top