W
weevilward
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the night. TNC-S, rewired couple of years ago (not by me).
Three circuits on this RCCB: Cooker, Downstairs sockets, Downstairs lights (I know - dumb layout…)
  • all tested for insulation resistance to earth at 250V (all >99M), also tested ins res between these circuits, all >99M;
  • earth leakage clamp revealed 7mA on cooker, 7mA on ring, and 2mA on lights. This was steady state. When first switched on, earth leakage spiked higher.
Couldn’t find a smoking gun so I put this down to either cumulative fault current, or an intermittent fault on an appliance. I reconfigured the board so these 3 circuits were on separate RCBOs, in the hope that either it would cure the problem or at least narrow down the search.
All fine for a week or so.
Then - phone call - both the cooker and downstairs sockets RCBOs had tripped simultaneously. And the lady thought the downstairs lights flickered a second or two before.
Any thoughts? I don’t know where to go next with this. I went back today and rechecked the insulation resistance and clamped for fault current - no change to the above.
It tripped again the same way this evening and this time they were 100% sure the lights went dim immediately before.
There’s no leakage between these circuits so how can two RCBOs be tripping simultaneously, and what is causing the lights to dim???
If I were to guess id say there is a low resitance between both L&N to earth on one of the circuits.. quite often the circuit effected wont trip as the imbalance is shared (both L&N) so the coil on the rcd wont trip.. it can creep ect other unrelated RCDs. Though
Whats going on with the forum having real trouble replying it's adding loads of spaces
make sure the neutrals are on the right rcds the other cause could be mice eating the cable which might account for the lights going dim
do a 500 volt insulation test make sure nothing is plugged in or switched to on like the boiler control
That makes sense but wouldn’t that show when testing insulation resistance between these circuits? I get >99MOhms L-L, L-N, N-L, N-N
Have you checked for crossed over neutrals?
Or one I had some years ago where there was an unterminated cable waaaay up high for an outside light that caused intermittent rcd issues, only tripped when it reined from a certain direction caused the end of the cable to get damp. took ages to trace
If it worked before, then it’s a new fault developed. Wrongly connected would show up straight away.
anything new been added to any of the circuits?
Smart meter? Long shot, but it’s happened before.
Individually, we might think an outside light or socket taking in water, or rodent damage… but for all 3 at same time?
What is the likelihood of rodents? Near fields?
Rodents - Very unlikely. Urban property. Kept immaculate. Recently gutted and refurbed (2 hrs ago ish)
Checked for crossed neutrals, it’s not that. Can’t rule out an unterminated cable somewhere but the tripping doesn’t link with rain. And that would only take out the one RCBO.
Ha, this house is full of tech! I wanted 500v test but there are smart switches, smart appliances, wall Mount TVs… I bottled it.
Surely the 250v test would reveal a problem ? All readings were >99M