I've been asked to install a meter between a c32 breaker and a 32A commando socket. I questioned there not being a breaker between the meter and the outlet but got some unprofessional abuse from the electrical designer. I don't know for sure that it isn't right but it just doesn't seem right. Can't find anything in the OSG and don't have my BRB away with me. A suggestion has been that the meter may prevent the mcb from operating correctly. Has anyone any thoughts? Anything appreciated!
 
I have never heared anything about the meter not making the mcb work correctly (though I have been wrong before).
It sounds ok to me, but I would stick a double pole isolator before the meter.
 
thanks Johno, I'm not trying to prove the (obnoxious little **** ) guy wrong but breaker then meter then oulet doesn't ring true. But , whatever, it's not my design. I'm trying not to get too sensitive, but I'm still the installer and if I don't ask the questions, who will?
 
Last edited by a moderator:
Jeremy the use of swear words will not be tolerated on the forums.
 
Last edited:
I've been asked to install a meter between a c32 breaker and a 32A commando socket. I questioned there not being a breaker between the meter and the outlet but got some unprofessional abuse from the electrical designer. I don't know for sure that it isn't right but it just doesn't seem right. Can't find anything in the OSG and don't have my BRB away with me. A suggestion has been that the meter may prevent the mcb from operating correctly. Has anyone any thoughts? Anything appreciated!

im my opinion there is nothing wrong with having the mcb before the meter. The service fuse is before the meter. The mcb will work fine. I dont see how you think it wont.
 
Sorry didn't mean to use naughty words. didn't even realise i'd done it. apologies to all concerned. Just seemed a bit "different" not having any isolation between meter and outlet and upon asking the question being told in effect that he would see me on the following tuesday, irked me slightly. Hope it is kosher as i energised it on Wednesday. PS arrive in Belfast on Tuesday for about 6 weeks if anyone fancys a beer. haven't been back in 16 years and could do with some pointers.
 
Sorry didn't mean to use naughty words. didn't even realise i'd done it. apologies to all concerned. Just seemed a bit "different" not having any isolation between meter and outlet and upon asking the question being told in effect that he would see me on the following tuesday, irked me slightly. Hope it is kosher as i energised it on Wednesday. PS arrive in Belfast on Tuesday for about 6 weeks if anyone fancys a beer. haven't been back in 16 years and could do with some pointers.

No probs mate the forum has to be kept clean as it is a public site.

Might be able to go for a pint in a few weeks when im home for a long weekend.

Are you from Belfast then?
 

Reply to unfused socket off sub meter in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
As per normal I was in a rush and didn't get enough information. I was working in an apartment that didn't have any power and when I went to...
Replies
8
Views
1K
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
856

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock