Discuss Unusual Sockets found on rewire in the Electrical Forum area at ElectriciansForums.net
Would that be standard socket on the left handside then the fuse to protect the round pin outlets on the right, say via a 5 or 3 amp fuse?
Is that around the introduction of the square pins, so you had sockets that took old and new for a while?
5 amp and 2 amp are still standard.......not 15amp, though.Some people still use the round pin style sockets to switch lamps on in a room from the main lighting with as you walk in to a room.
5 amp and 2 amp are still standard.......not 15amp, though.
Like this lot go to Theatres.........Umm, 15A is very standard if you are in a theatre ...
Umm, 15A is very standard if you are in a theatre ...
Aye, and all wired in vir, just like the domestic stuff in question, I suppose.Umm, 15A is very standard if you are in a theatre ...
Like this lot go to Theatres.........
When those were put in, the regs (e.g. 14th ed. of 1966) specified a CPC one size down from the L & N for many sizes of T+E. Therefore. 7/.029, the standard cable for rings before 2.5mm², had a 3/.036 CPC, equating to 3.0mm² with a 2.0mm² CPC. The three smallest cables, 1/.044, 3/.029 and 3/.036 all normally had a 1/.044 CPC however.all wired in pvc with stranded conductors (even the earth were three strands).