Adzg91

Hi there,

I'm attempting to replace our wall mounted outdoor light and when I went to remove the wiring it looked a little off.

Coming from the wall are 2x black, 2x red and 2x earth. The red wires are connected to form a loop. One black to live connection and one black to neutral connection.

My expectation was that live to live, neutral to natural so I'm a little stumped.

Any advice would be appreciated.

Thanks,

Adam
 
standard loop in wiring. the 2 reds go together but not to the light. 1 black is Neutral ut the other black is switched Live. so connect the 2 reds tohether in a connector. then the 2 blacks go to the light. 1 to each terminal. to be pedanticc the switched L should be over sleeved red. the 2 cpc's (earths should be connected togeter; if there is an earth terminal on the light fitting, use it.
 
standard loop in wiring. the 2 reds go together but not to the light. 1 black is Neutral ut the other black is switched Live. so connect the 2 reds tohether in a connector. then the 2 blacks go to the light. 1 to each terminal. to be pedanticc the switched L should be over sleeved red. the 2 cpc's (earths should be connected togeter; if there is an earth terminal on the light fitting, use it.
Thanks so much! This really threw me and I was surprised (my electrician knowledge isn't the best and I was expecting a similar setup to plugs).

Can you please explain what you mean by "to be pedanticc the switched L should be over sleeved red."?

Thanks again!!
 
basicaly, the switch wire is T/E which comes in red/black, so that's why the black( which is switched L) shuld be sleeved. twin red T/E is /was available but not so common. all changed now, it's brown/blue. another clever move by the IET (was (IEE) to confound and confuse , thus making more money for amendments to the regulations.
 

Reply to Unusual wiring on outdoor light in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
417
Hello everyone, hope all are well. I'm changing a ceiling rose and have lost the diagram showing where everything was connected (to the old light)...
Replies
8
Views
904
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
863
I have 2 lights connected to 1 switch. I installed a led light fixture on one light, it had one red wire and one black wires. It was easy to match...
Replies
0
Views
265
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock