Hi

Recently we were asked to put in an 80A 3 phase supply to a UPS system, we carried out the work to the manufacturers guidelines with an 80A mccb in the panel board. To much annoyance of all the office workers, when the supply was turned on it blew all 3 of the main fuses that are rated at 100A.

Has anyone had any similar problems?
 
Single phase links left in?!!

What other loads are connected? An additional 80 amp load connected might be too much for the 100A supply, but I wouldn't expect the fuses to blow instantly, unless the supply was already overloaded.
 
Do you mean inside the the actual ups box? We didn't install that part so that could be! Wouldn't you expect the 80A mccb to trip first with that kind of fault conditions?

That was my first go to that they were overloading their supply but with load tests they are pulling 40A per phase so it's not too bad
 
I'm not intierly sure to be honest when I get back to the office tomorrow I'll find out. There is 10 seperate ups backups but we were just given a 5c 10mm flex that needed a supply.
 
If there are 10 separate modules in the UPs it more than likely not an AP Emerson type as they usually come in 7.5 10, 15 KW etc
 
Yea I'm not to sure on the specs of the ups I just no it's quite a large set up. It's is used to keep the mainframe computer racks going during power failure such as what happened when we turned it on
 
That is at the same place as this ups. It's one of the most rediculous things 20 twin sockets per length and there is 3 of them in the same room!
 
Hi

Recently we were asked to put in an 80A 3 phase supply to a UPS system, we carried out the work to the manufacturers guidelines with an 80A mccb in the panel board. To much annoyance of all the office workers, when the supply was turned on it blew all 3 of the main fuses that are rated at 100A.

Has anyone had any similar problems?

as the load will be highly inductive, then the load will be very re-active.
Sort of like a start up surge on an electric motor.
You might need to use breakers with a time lagg
such breakers are used on electric motors and
are designed to cope with a large but short start surge.
the term used in Australia is "slow-blow'.
 

Reply to UPS supply problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We are looking for a distribution board to provide 3 * 160A three-phase feeds, but they are basically redundant supply path options so max total...
Replies
4
Views
269
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Hi I have UPS 50KVA and the inverter output AC voltage is feeding a distribution panel 120/208 V 4 wires when I check UPS display it shows me...
Replies
1
Views
241
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock