Perci

-
Joined
Aug 25, 2014
Messages
29
Reaction score
14
Location
Melton Mowbray
Hi

Recently we were asked to put in an 80A 3 phase supply to a UPS system, we carried out the work to the manufacturers guidelines with an 80A mccb in the panel board. To much annoyance of all the office workers, when the supply was turned on it blew all 3 of the main fuses that are rated at 100A.

Has anyone had any similar problems?
 
Single phase links left in?!!

What other loads are connected? An additional 80 amp load connected might be too much for the 100A supply, but I wouldn't expect the fuses to blow instantly, unless the supply was already overloaded.
 
Do you mean inside the the actual ups box? We didn't install that part so that could be! Wouldn't you expect the 80A mccb to trip first with that kind of fault conditions?

That was my first go to that they were overloading their supply but with load tests they are pulling 40A per phase so it's not too bad
 
If there are 10 separate modules in the UPs it more than likely not an AP Emerson type as they usually come in 7.5 10, 15 KW etc
 
Yea I'm not to sure on the specs of the ups I just no it's quite a large set up. It's is used to keep the mainframe computer racks going during power failure such as what happened when we turned it on
 
Hi

Recently we were asked to put in an 80A 3 phase supply to a UPS system, we carried out the work to the manufacturers guidelines with an 80A mccb in the panel board. To much annoyance of all the office workers, when the supply was turned on it blew all 3 of the main fuses that are rated at 100A.

Has anyone had any similar problems?

as the load will be highly inductive, then the load will be very re-active.
Sort of like a start up surge on an electric motor.
You might need to use breakers with a time lagg
such breakers are used on electric motors and
are designed to cope with a large but short start surge.
the term used in Australia is "slow-blow'.
 

Reply to UPS supply problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
289
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
672
  • Question
Useful to know. In my case there will be 150x150mm trunking at top/bottom and almost certainly I will be using tri-rated cable, probably 70mm...
Replies
4
Views
534
  • Question
I recently had similar but my 2 supplies were from different transformers going into different ends of a long property divided in two. Western...
Replies
11
Views
2K
  • Question
Distribution network operator set there are in standard. It depends on what the material of the cable is in case it’s copper or aluminium but they...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks