Hi, quick question…
Just moved into a new house and have been replacing some damaged metal sockets / faceplates with plastic versions … anyway, removed a 1 gang metal blanking plate and found 1No. old (red/black) 2.5mm with exposed copper inside the box (token bit of tape long since dried up and fallen off the ends) - this was still live, and only a couple of mm from the faceplate. Traced the cable to a 2 gang socket in the next room (ie whatever was at the now-blanked box (probs storage heater) was a spur from this socket. NB - spur definitely dead when disconnected from this socket).
Two questions, given I can’t remove this cable:
1. Assume it’s ok to just put 3no. Wagos (L,N,E) on the wires in the blanked box to render this end safe?
2. Is it acceptable to disconnect the spur cable from the socket also, put 3no. wagos on this end too, and have these wagos ‘loose’ in the socket back box (ie spur cable fully disconnected, but cable and wagos left within the same back box as the still-live socket?).
Just want to do neat and safe job…
Obvs interested in any neater / better recommendations… eg crimps plus heat
Cheers
TL;DR
Can I terminate a redundant cable with wagos inside a live socket back box…?
Yes you can use wagos to terminate the unused cable and refit the blanking plate.
Likewise you can use wagos to terminate the disconnected spur cable at the socket as long as there is room to fit it in the box. It would be sensible to label that cable to help the next person to understand what it was for.
If it is going to remain live the earth must be connected to either the back box (if a plastic plate is to be fitted) or the front plate (if a metal plate is to be fitted).
Hi, quick question…
Cheers
You could use single Wagos or ideal single push fit to terminate the cables, giving you more space
Thanks for the reply - very useful. Cheers
Thank you, very helpful - I did wonder about that but couldn’t see a screw terminal in the back box, but maybe I just need to clear out some of the plaster detritus and look harder. I think ideally I won’t keep it live, feels inherently safer given it’s likely (based on positions of socket and blanking plate) that the cable isn’t entirely in the protected zones of either (although the circuit is rcd protected at the cu).
Thanks again.
Could you repurpose the blanked off box as a single socket?
If it was, as you think in OP, a storage heater... then this supply would come direct from an off peak heating board, and not the ring circuit...
Are you certain the cable is fed from this other socket? Have you dead tested continuity?
Thanks for reply - very helpful / useful thoughts...
So re. repurposing as a socket... it's in a slightly odd position near a radiator so wasn't first thing I thought of, but it would be an option (although the cable ends in the back box are too short to wire to a socket directly, so I'd need to extend the wires).
Re. storage heater ... good point, there is / was an off peak board that is totally disconnected, and there is a lot of redundant wiring that was associated with this - so yes, now you've made me think about it properly it's perhaps unlikely to have been storage heater (unless the box was repurposed as a spur after the heaters were removed... although that doesn't feel that likely) - however, I have dead tested continuity and it's definitely a spur from the other socket...
Thanks for your help - much appreciated.