yes lol coz I had job last year nothing working but had polarity, measured 155 v on the screws passed over to DNO joint had gone down in street.
 
yes lol coz I had job last year nothing working but had polarity, measured 155 v on the screws passed over to DNO joint had gone down in street.

Now this makes more sense. Nothing working which l didn't think it would....
 
Never mind the IET and EU harmonisation.

The specification for a DNO local transformer is for up to 1000KVA, 11/.433KV 4.5% reactance. 1500KVA the reactance rises to 5%

433V not 400V
 
You could always do the good old way a taste to see what flavour voltage it is 230 or 400. :p

Which planet are you on?

230 = 400/√3, to all intense and purpose the same.

Which flavour of vanilla?

If you really want to be pedantic 230.94 = 400/√3
 
No idea what you're all arguing about you'll never going to be seeing 230 Volts or 400 volts in the UK or Europe for literally 10's of years, if ever!! lol!! It's all just fantasy world stuff!!
 
It could be done using the voltage regulators on the 33KV OLTC’s. The knock on would be disastrous. The LV network can’t cope with the current loading as it is now.

I tried lowering the voltage on an 80MVA system, I soon put it back to where it was.
 
If you want to be really pedantic 230*√3 = 398.37


:-)

4_14_6.gif
 
What do the IET expect to happen where this occurs? Im a little confused here. If l listen to my maths teachers from sparky college, he said that a voltage drop can cause a circuit to overload.

Is that whats happening here, at the transformer perhaps? Ive no idea personally and would love to know the answer as ive never seen 223V anywhere before. Always been 236-253V...

I think your maths teacher needs to think about this "overload" comment, it's simply incorrect. A drop in the voltage will cause the load to decrease.
 
This guy above is correct , as I've been put right before and explained too .. Burning forget.

but I'd say its a misunderstood equation , higher voltage = lower current ..
 
I think your maths teacher needs to think about this "overload" comment, it's simply incorrect. A drop in the voltage will cause the load to decrease.

Time you learnt about workload and efficiency. Not every load is resistive, in fact most aren’t.
Take a motor, input power = output power – efficiency.

1KW at the shaft needs 1KW feed in to the motor and a bit more for the losses.

1KW = 1000W no mater how you look at it.
 
Time you learnt about workload and efficiency. Not every load is resistive, in fact most aren’t.
Take a motor, input power = output power – efficiency.

1KW at the shaft needs 1KW feed in to the motor and a bit more for the losses.

1KW = 1000W no mater how you look at it.

This is the same as another post in which this came up. Items on electrical equipment are given a power rating according to a nominal voltage, they do this as voltages are never constant.

With no voltage applied a motors windings are a theoretical linear load, once voltage is applied the load becomes inductive and so the impedance opposes the flow of current and and limits it. Even with no rotor, a motors windings will limit the flow of current.

Once a rotor is introduced, the windings induce a voltage (and so a current) within it and as the sine wave of the supply voltage fluctuates at the given frequency, the rotor tries to keep up. As the load on the motor is increased, the slip of the rotor increases also and with this there is a greater difference in speed between the supply frequency and rotor, creating a larger current in the rotor.

With these points made, how would a lower voltage on a given size of motor result in a greater current? What happens if a 240V voltage is placed across the coil of a 24V relay? The relay will have a stated holding current at its nominal voltage (24V) but applying 240V won't reduce this current ten fold to keep the coil power consumption constant.

Although a motors load may indeed be constant at 1kW, this does not mean the voltage and current will flex to meet this fixed load. A motor may be capable of providing the torque to meet a load of 1kW at a given geared speed negating the slip. This very same motor may be incapable of generating the torque at a few volts less as it would simply stall if the voltage was not high enough to generate a high enough current to drive the load before losses.

If a motor is loaded at 100% of its rating, it must be supplied with its rated nominal voltage or higher to drive the load. A lower voltage will not just simply result in a constant power output through an increased current.

I think the time for me to learn has passed and it is you who needs more time to learn.
 