With these points made, how would a lower voltage on a given size of motor result in a greater current? What happens if a 240V voltage is placed across the coil of a 24V relay? The relay will have a stated holding current at its nominal voltage (24V) but applying 240V won't reduce this current ten fold to keep the coil power consumption constant.
This is a non-sequitur because a motor is not the same as a relay coil.
A relay coil has constant impedance at a given frequency because it is a simple RC series network, therefore its current will be approximately proportional to the voltage (ignoring magnetic non-linearities). Note that the electrical power absorbed at a given voltage is determined mainly by the characteristics of the coil.
A typical AC motor is a much more complex animal. Its stalled-rotor impedance is relatively low, therefore the electrical power absorbed at a given voltage is determined not so much by the characteristics of the motor but those of the load. I.e. it does not look like a constant impedance from the electrical side.
For synchronous and induction motors, within sensible limits that do not cause the motor to stall, the variation of speed with voltage is zero or small. For any conventional load torque-speed curve the variation of torque with voltage is thus also zero or small, hence also the output power. But as the voltage changes, so do the load angle and power factor. It is necessary to know the characteristics of the motor to determine precisely how the current and power factor will vary with voltage at constant torque, however the in-phase component of the current must vary inversely with the voltage and can be calculated from the input power as Tony points out above.
A more clearcut case occurs with a power-factor-corrected switched-mode power supply that operates at constant efficiency and constant output voltage. That most certainly does have negative dynamic resistance, and will consume current inversely proportional to the voltage, within the range of voltages it will accept.