Discuss Volt drop in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Hi I've a few questions regarding volt drop. Apologies if its a little longwinded but I'd like to get my head around everything.


An example scenario is a section board with a TP sub main to lighting and power board (DB2)

Calculations for circuit :


Supply Voltage = 400 Volts
Ib - Design current = 63 Amps
Protective Device Type = 63A MCB type B (BS EN 60898)
Cable Type : Thermosetting ARMOURED 90°C - Multicore
Length of run of cable = 100 metres

Lets assume there are no correction factors.
I've decided to go with a 16mm SWA so from TABLE 4E4B mV/A/m = = 2.5

Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 2.5 x 100 x 63 ) / 1000
Voltdrop = 15.75 Volts


Now my first set of questions are:


- Do I use 63amp for the volt drop (as this is what the cable COULD carry at some point)? or use actual figures from DB2 which would be less?
- If I use actual values how do I work this out when its unbalanced loads?
- I've read that as a rule of thumb only 1.5% VD should be lost for sub mains. So 400/100 * 1.5 = 6v


So if this 1.5% rule is correct I deceide to put a bigger cable in, let's say a 70mm


From TABLE 4E4B mV/A/m = = 0.87

Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 0.87 x 100 x 63 ) / 1000
Voltdrop = 5.48 Volts


So far does this look correct?


Now at DB2 I have a few circuits

1/L1 - (20 x 33w LED panels. So 660/230 = 2.9A
1/L2 - (30 x 33w LED panels. So 990/230 = 4.3A
1/L3 - (25 x 33w LED panels. So 825/230 = 3.6A


I've been told that when working VD from a 400v to 230v supply I use the following correction factors.
(x 0.866) Assumes there is some current in the neutral.
(÷ 2 Assumes a balanced circuit with no current in the neutral.


So its an unbalanced load (x 0.866)

Volt drop for the lighting circuit would be 230/100 * 3 = 6.9v


Circuit 1 is 20m long

Again assuming there are no correction factors:

TABLE 4D5 For 1 mm²: mV/A/m = 44
Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 44 x 20 x 2.9 ) / 1000
Voltdrop = 2.55 Volts


Total volt drop from orogin to end light

Sub main = 5.48 x 0.866 = 4.7v
Lighting circuit = 2.55

Total VD = 4.7 + 2.55 = 7.25v (too high)


Next size up
TABLE 4D5 For 1.5 mm²: mV/A/m = 29
Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 29 x 20 x 2.9 ) / 1000
Voltdrop = 1.68 Volts


Total volt drop from orogin to end light
Sub main = 5.48 x 0.866 = 4.7v
Lighting circuit = 1.68

Total VD = 4.7 + 1.68 = 6.38v
Does this look correct?


A few other general questions:
- I've read if its designed at only 30%. so 3A for a circuit thats 10A mcb no correcion factors apply. Is this correct?
- Also how is a socket circuit designed? Becuase its very unlikely that 32Amps will be used,
 
start with the load (including projected additions) on each sub to get a realistic value of Ib for your distribution. then if each sub is all single phase loads, work out the VD per phase @ 240V. much simpler.
 

Reply to Volt drop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
725
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
I'm getting a little confused about volt drop and 24v. I want to fit an LED strip light. 8m of lights 7w/m. It would be easier to have the 24v...
Replies
13
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock