luke12345

Hi I've a few questions regarding volt drop. Apologies if its a little longwinded but I'd like to get my head around everything.


An example scenario is a section board with a TP sub main to lighting and power board (DB2)

Calculations for circuit :


Supply Voltage = 400 Volts
Ib - Design current = 63 Amps
Protective Device Type = 63A MCB type B (BS EN 60898)
Cable Type : Thermosetting ARMOURED 90°C - Multicore
Length of run of cable = 100 metres

Lets assume there are no correction factors.
I've decided to go with a 16mm SWA so from TABLE 4E4B mV/A/m = = 2.5

Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 2.5 x 100 x 63 ) / 1000
Voltdrop = 15.75 Volts


Now my first set of questions are:


- Do I use 63amp for the volt drop (as this is what the cable COULD carry at some point)? or use actual figures from DB2 which would be less?
- If I use actual values how do I work this out when its unbalanced loads?
- I've read that as a rule of thumb only 1.5% VD should be lost for sub mains. So 400/100 * 1.5 = 6v


So if this 1.5% rule is correct I deceide to put a bigger cable in, let's say a 70mm


From TABLE 4E4B mV/A/m = = 0.87

Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 0.87 x 100 x 63 ) / 1000
Voltdrop = 5.48 Volts


So far does this look correct?


Now at DB2 I have a few circuits

1/L1 - (20 x 33w LED panels. So 660/230 = 2.9A
1/L2 - (30 x 33w LED panels. So 990/230 = 4.3A
1/L3 - (25 x 33w LED panels. So 825/230 = 3.6A


I've been told that when working VD from a 400v to 230v supply I use the following correction factors.
(x 0.866) Assumes there is some current in the neutral.
(÷ 2 Assumes a balanced circuit with no current in the neutral.


So its an unbalanced load (x 0.866)

Volt drop for the lighting circuit would be 230/100 * 3 = 6.9v


Circuit 1 is 20m long

Again assuming there are no correction factors:

TABLE 4D5 For 1 mm²: mV/A/m = 44
Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 44 x 20 x 2.9 ) / 1000
Voltdrop = 2.55 Volts


Total volt drop from orogin to end light

Sub main = 5.48 x 0.866 = 4.7v
Lighting circuit = 2.55

Total VD = 4.7 + 2.55 = 7.25v (too high)


Next size up
TABLE 4D5 For 1.5 mm²: mV/A/m = 29
Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 29 x 20 x 2.9 ) / 1000
Voltdrop = 1.68 Volts


Total volt drop from orogin to end light
Sub main = 5.48 x 0.866 = 4.7v
Lighting circuit = 1.68

Total VD = 4.7 + 1.68 = 6.38v
Does this look correct?


A few other general questions:
- I've read if its designed at only 30%. so 3A for a circuit thats 10A mcb no correcion factors apply. Is this correct?
- Also how is a socket circuit designed? Becuase its very unlikely that 32Amps will be used,
 
start with the load (including projected additions) on each sub to get a realistic value of Ib for your distribution. then if each sub is all single phase loads, work out the VD per phase @ 240V. much simpler.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Volt drop
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
luke12345,
Last reply from
telectrix,
Replies
1
Views
1,542

Advert