drzsta

-
Arms
hi all,

I have a situation where I would need to supply a 40kW installation from a Generator situated 300 meters away (not ideal). As this is a private LV supply up to 8% VD is permissible as per App. 4 Sect 6.4 in the BYB. However it then goes on to state that final circuits should not exceed public LV supply values of 5%.

The way I am interpreting this is that I can have up to 8% on my distribution cable to the origin of the installation(the DB) then a further 5% for final circuits.

This would lead to a possible situation of 348V L-L at the furthermost point in the installation if it did not contain lighting ccts.

Is this how others interpret it with respect to Section 525?

cheers,
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

drzsta

Arms
-
Joined
Location
out in the cold
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Volt drop..................................................
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
drzsta,
Last reply from
drzsta,
Replies
2
Views
1,195

Advert

Back
Top