hi guys
Need some help in calculating voltage drop on a branched radial circuit. (13A design load 2.5mm cable)( cu to junction box 8m 2.5mm)
for a standard loop in loop out radial it would be IbxDxmV/m/1000
this circuit has 2 branches from the junction box
one/ 10m long ( 1 double socket)
2nd 27m long ( 3 double sockets)
can any one help re Volt drop
easy. calculate the VD at the junction using the sum of the Ib 's of each branch. then calculate each branch and add on to get the 3 values.
Need more info, anticipated load, OCPD type, installation method etc etc
thanks tel. so if each branch has a design load of 13Amps then the volt drop at the Junction box would be , 13+13x8x18/1000 = 3.74v
branch 1) 13x10x18/1000 = 2.34
branch 2) 13x27x18/1000 =6.318
to note desgin load total circuit 13A
is my thinking correct ??
not quite. if your OCPD is 16A, then that's your max. Ib for the circuit. likewise if it's 20A then your Ib is 20A (max.).
Reply to Voltage Drop Branch of radial circuit in the UK Electrical Forum area at ElectriciansForums.net
I found a 13A FCU, connected to the kitchen ring supplying an outdoor junction box, providing two SWA 2.5mm radials. Unconventional? yes. One...
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...