Without going in to my calculations and design details (just yet), I have a customer wanting a supply to a summerhouse and workshop which is approx 100m from the source.
My calcs call for a 16mm² feed to overcome voltage drop, well O.T.T for the required Ib but non the less, what it comes out at. Spoke to NAPIT as it is borderline 10mm² feed and they said if the supply voltage is steady and measured at peak, I could use this in my calc rather than the supply nominal voltage.
Is this acceptable as I can't see anything in the regs that permits this. However, I can't see anything that doesn't. 236v at source would allow for a 10mm² feed.
Just remember your lighting in the summer house still requires a voltage drop of no more than 3% of 230 volts.
The nominal voltage of 230v does often lead to oversized distribution circuits at times but errs on the side of caution.
Quite often round my neck of the woods the voltage when measured is usually around 245 volts which gives me an extra 15 volts to play with but at peak times that voltage may well drop off a bit.
Also if your doing calculations on 16mm remember that if the cables not running at full load you will won't have the full voltage drop on the cable as it won't be running at 70 degrees.
If you are borderline on being able to use 10mm² and your calculations do not include corrections for underloaded cables then the above should allow you to use 10mm².
I would not use the actual voltage as this may not be stable over the long term. You are unlikely to have any problems with a low voltage for a domestic situation.
Reply to Voltage drop in domestic installation in the UK Electrical Forum area at ElectriciansForums.net
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Hi all, I am currently doing my 2391-52 and have been given a mock paper, one of the questions is around vold drop as per below, can someone...
5K
I have my tin hat on because I know this has been done to death and have read through a lot of the old posts. I just wanted to run my proposal...
7K