Discuss Voltage drop in domestic installation in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
116
Without going in to my calculations and design details (just yet), I have a customer wanting a supply to a summerhouse and workshop which is approx 100m from the source.

My calcs call for a 16mm² feed to overcome voltage drop, well O.T.T for the required Ib but non the less, what it comes out at. Spoke to NAPIT as it is borderline 10mm² feed and they said if the supply voltage is steady and measured at peak, I could use this in my calc rather than the supply nominal voltage.

Is this acceptable as I can't see anything in the regs that permits this. However, I can't see anything that doesn't. 236v at source would allow for a 10mm² feed.
 
Just remember your lighting in the summer house still requires a voltage drop of no more than 3% of 230 volts.
The nominal voltage of 230v does often lead to oversized distribution circuits at times but errs on the side of caution.
Quite often round my neck of the woods the voltage when measured is usually around 245 volts which gives me an extra 15 volts to play with but at peak times that voltage may well drop off a bit.
Also if your doing calculations on 16mm remember that if the cables not running at full load you will won't have the full voltage drop on the cable as it won't be running at 70 degrees.
 
Also if your doing calculations on 16mm remember that if the cables not running at full load you will won't have the full voltage drop on the cable as it won't be running at 70 degrees.
If you are borderline on being able to use 10mm² and your calculations do not include corrections for underloaded cables then the above should allow you to use 10mm².
I would not use the actual voltage as this may not be stable over the long term. You are unlikely to have any problems with a low voltage for a domestic situation.
 

Reply to Voltage drop in domestic installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
831
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
520
Hi Doing my first Inverter and Battery install on a domestic property having just completed my EESS course with LCL. Question is how do I...
Replies
19
Views
6K
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Replies
4
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock