A

apple123

Hi

I have been called in (I know I should know better) after a guy who did an EICR reported some IR issues and then scarpered. When I went to repeat the test I got a shock of the a lighting CPC ( measured at 115 volts) I have removed the covers from outlets all seem OK, have split the circuit to nail down where the problem is and it would seem to be somewhere at the beginning of the circuit. Before I start pulling up carpets and floorboards anybody got any ideas what else I can check. FYI There are a lot of metal face plates on the switches.
 
What IR results did you get?
WHere abouts on the circuit did you measure the voltage?
Why has the customer not mentioned getting a electric shock?
Do all the lights work correctly?

Sounds like a CPC could be being used a the neutral
 
Hi

I have been called in (I know I should know better) after a guy who did an EICR reported some IR issues and then scarpered. When I went to repeat the test I got a shock of the a lighting CPC ( measured at 115 volts) I have removed the covers from outlets all seem OK, have split the circuit to nail down where the problem is and it would seem to be somewhere at the beginning of the circuit. Before I start pulling up carpets and floorboards anybody got any ideas what else I can check. FYI There are a lot of metal face plates on the switches.
First thing to do is remove all lamps and transformers on the circuit put all switches on and meggar between L-N, L-E, N-E on the 500 volts scale and see whats actually there, make sure nothing electronic is connected to the circuit and make sure you disconnect the circuit from the DB
 
Can't find earth neutral connection, got .25 Live/ earth IR >200 Live/Live measured st the board (BS3036) all lights working well.
 
Yes did that part from one transformer the client buried beneath some wood cladding, tackle that one tomorrow.
 
before IR testing, i'd start with a wander lead and perform R2 test from DB to all metal fittings on the circuit and to the E terminals on any plastic fittings.
 
Just finished the job all tested ok, mixture of problems, found a light outside with N in earth, couple of screws through cable last but not least floorboard nail through notched joist.

Thanks for everyones input it helps to talk it through sometimes.
 
There panic over sounds like you didn't even need us and a notch on your fault finding experience ;)
 