Hi folks,

One year ago I was I asked to fit a voltage optimisation unit, the very popular one. Now it is the time to share some results.

Customer's annual electricity consumption, before the unit was installed, was the following:

17 January 2007 to 7 February 2008: 8,375 kWh
7 February 2008 to 14 February 2009: 7,711 kWh
14 February 2009 to 4 February 2010: 7,279 kWh
4 February 2010 to 1 February 2011: 7,730 kWh

These averaged to 7773.75 kWh

The unit was fitted on the 9th of April 2011.

The electricity consumption from 1 February 2011 to 31 January 2012, with the unit performing for the last 10 months of this period, was recorded as 6,990 KWh.

Savings:
7774 - 6945 = 829 kWh
829 / 7774 = 10.7%

Other facts:

2-person household, a couple close to retirement age. Home cooking and office work.

Gas heating, electric shower, electric cooker, around 1/3 of the lighting: fluorescent bulbs, some energy saving bulbs, some halogen lighting, freezer in the garage, LCD TV, computers.

Experiences of the lights brightening when the unit was switching to by-pass mode.

The voltage measured during the by-pass mode operation varied from 235V to 249V.

End.
well i`m sorry but the only evidence i would accept is under laboratory condidions...that is to say that load was monitored...
all connected loads were supervised and any replacement/new appliances were logged/taken into account....
anything else is heresay and rubbish.....
 
Your years' up!
Update please :)
You marked this thread on your calender didn't you :)

I'm not a complete nay sayer when it comes to voltage optimisation but the problem for me is how on earth would you obtain reliable statistics without, as Tony suggested a year ago, you set up two identical houses one with an optimiser and one without and rig them so the load on them is identical at all times. Until this happens there's way too many variables to give meaningful and comprehensive results and figures.
 
I can see them being viable in say a decent sized supermarket type situation, where there is a significant numbers of freezers, fridges, cold store cabinets, central Air con units and large numbers of Flu lighting fittings etc. I'm certainly not convinced with domestic type VO's, (especially the V phase unit, that thing will spend more time on by-pass than on line!!) where i can see pay back taking several years. Far better IMO to replace every lamp in the house with LED lamps, your return will be far quicker!! lol!!
 
I can see them being viable in say a decent sized supermarket type situation, where there is a significant numbers of freezers, fridges, cold store cabinets, central Air con units and large numbers of Flu lighting fittings etc. I'm certainly not convinced with domestic type VO's, (especially the V phase unit, that thing will spend more time on by-pass than on line!!) where i can see pay back taking several years. Far better IMO to replace every lamp in the house with LED lamps, your return will be far quicker!! lol!!
well i remember at last years elex show they were busy tryin to flog these things....
i noticed then that any high loads would send the unit into bypass....and it wasn`t much either...
as you say...energy saving equipment would be the better choice...and return...
 
I didn’t see V Phase at this years Harrogate Elex. Had they been there I would have cheered up because I enjoy baiting company “technical” salesmen.

Would love to be a fly on the wall listening to that conversation!! lol!!
 
There are Ofgem / Energy saving Trust and RWE / NPower reports available covering home installtions.

We do a lot of large commercial work and for the big userss (no bypasses here :) ) they have all seen significant savings, and generally the equipment seems happier, then only exectpion where we saw one group of installtions where they clearly hadn't measured the incoing as the 3 pahse outgoing was around 360V ...

For large commercial users, it ALMOST always make sense, however if you do other energy saving measures you can yield just as good results.

For the home, the reports are here:
https://www.electriciansforums.net/...report-20for-20the-20vphase-20vx1-pdf.120378/
and here
http://vo4home.com/_literature_38090/RWE_Npower_trial_report


The Voltis and Vpahse units both go into bypass modes and when mixed with Solar PV generations and evening loads, they can interesting effects on the lights and equipments as they go in and out of bypass mode.
The V04Home units is a full load unit with no bypass needed - you pay for that though as the price is 50%-100% more than the others.

Until more long term results are available, my feeling is that the Jury is still out. Having said that a customer has just asked us to install a V04Home unit for him and we didn't even approach or 'sell' the idea yo him, so we are going to do it next week for him and well see what the results are as time goes on.

I would expect that as people put in the measures they start to adopt energy saving approaches to how they use eneregy anyway, so it would also be interesting to see a 'double blind' test with a Placebo unit (aka sealed empty box :) ) to see if that alone also has an effect. (quite like that idea, install an empty box, charge £500 for it and tell them it will helo them save energy :jester:.. ) [Perhaps I should go work for BG !!!]
 

Attachments

Vo4Home unit has a retail price of £599 plus VAT plus installation (Ouch :) )
You should be able to get one supplied and installed for that price i.e. about £750 inclusive (so long as not lots of mods needed to incoming tails).
Unfortunately it attracts 20% VAT .
 
Vo4Home unit has a retail price of £599 plus VAT plus installation (Ouch :) )
You should be able to get one supplied and installed for that price i.e. about £750 inclusive (so long as not lots of mods needed to incoming tails).
Unfortunately it attracts 20% VAT .


That's just totally silly money for a domestic installation.... I can't see how they can justify that sort of money to be honest!!
 
Yeah, that strikes me as a large capital outlay that would possibly/probably take many many years to pay back even the principal amount, never mind the interest it would have earned if it was in a bank account. I can see many ways a domestic customer could spend that sort of money and get a far larger return on the outlay. I think I'd only be considering one of these units as part of the final phase in a much larger and holistic energy saving plan.
 