We had our kitchen done 5yrs ago and we've just had to replace our Tumble Dryer and found that there is a double socket under the sink that supplies both the Washing Machine and Tumble Dryer.
It's worked fine for 5yrs, but it was highlighted by the guy that installed it (part of taking the old one away) that it wan't "ideal".
There's conflicting stuff on the net about this, so just thought I'd post for a bit of clarity?
From my research, double sockets are rated up to 20 amps for a minimum of 4 hours. I've checked the wattage of both appliances and converted to amps as follows:
Washing Machine = 1600W or 6.96 amps
Tumble Dryer = 2200W or 9.57 amps
Does that mean with both appliances on at the same time, the max draw would be 16.13 amps and well within the 20 amp rating of the double socket? Notwithstanding that the Washing Machine will only draw max power for 15/20 minutes of each wash?
Just to be safe, we are intending not to run the both of them at the same time, but would be "safe" in any event?
Although it would be better to have 2 single sockets, it’s unlikely that your current setup will be a problem.
I have seen this particular set up fail but that was a washing machine and dishwasher plugged in, possibly higher load ratings.
Changing the 1 double socket to 2 x singles would increase the permitted load on each, but depending on how it is wired, it may fall foul of the “no spur from a spur” regulation.
As James has said, it’s unlikely to cause a problem as it is, if it hasn’t up to now…
I would agree, unlikely to cause a problem. Last house it was like that for nearly 20 years, without a problem. This house I carefully arranged it, so the two were drawing from different circuits, then changed the dryer, so now only drawing 650 watts for the dryer anyway, and the washer only draws maximum for around 5 minutes at a time.
I went for a heat pump condenser dryer to replace the vented type, mainly so I could close the window which the pipe went out of, and an air cooled condenser would make the room rather hot, and could only find water cooled when combined with the washing machine, so the refrigeration heat pump would reduce how hot the room got.
As to running cost, old vented dryer had a 1 kW and 2 kW setting, always used the 1 kW setting, and it did not have as big as a drum to heat pump version, so with a large wash would need to run it twice, but normally ran for 90 minutes, some times would need a second dry, so basically the running cost heat pump to vented were nearly the same, and the heat pump takes longer, so I am sure if we had the option to set vented to 650 watts they would be the same.
The problem with the air cooled condenser dryer, is there is no option to turn down the power used you have to run at 2 kW, and the water cooled one we have in our flat, gets the clothes far too hot.