A = Protection against AC earth fault currents containing pulsating DC components
B = Protection against DC earth fault currents
AC = Protection against AC earth fault currents
S = Delayed
Where is this field? Do you mean on the schedule of test results? If so, the BS EN field is for overcurrent device, not RCD!
If being used as a main switch, then just put down BSEN 61008-1. The RCD "type" is irrelevant, just put a dash!
Yes but the over current device just require type and In, The BS number will be required on the EIC which can either be put in the characteristic of the supply and earth section or Main Switch or Circuit Breaker section, where the RCD would be noted if it is used main circuit breaker.