He is also testing at a socket with such a short piece of cable that it would make no real difference to the test. Imagine that cable as being a realistic length for a final circuit and work out how it may affect the result.
Yes I see what you mean, thanks for replying.
I've just wandered into this post, TBH I haven't got the level knowledge to agree or disagree with anyone.:smiley2:

Can you clarify if I'm doing it right.
MF tester on RCD
Auto - 30ma selected.(appropriate)
I stick a probe in the top of the closest protected MCB to the RCD
Probe to the N of that circuit and EARTH.

After that I record the readings, do a ramp test, and press the test button.
Signed: Confused of Sussex ! :mickey:
 
Kurtis I guess as you test at the circuit and not the RCD itself, do you perform the RCD test for/on every circuit and mark each and every result down on your cert?
 
Last edited by a moderator:
Yes I see what you mean, thanks for replying.
I've just wandered into this post, TBH I haven't got the level knowledge to agree or disagree with anyone.:smiley2:

Can you clarify if I'm doing it right.
MF tester on RCD
Auto - 30ma selected.(appropriate)
I stick a probe in the top of the closest protected MCB to the RCD
Probe to the N of that circuit and EARTH.

After that I record the readings, do a ramp test, and press the test button.
Signed: Confused of Sussex ! :mickey:

Not quite.

You switch off all MCBs protected by it, and drop the outgoing N connection from the RCD.
Clip on to an earth connection and probes on the outgoing terminals of the RCD with firm contact pressure.
Start the test.
You can remove L and N probes between each test to reset the RCD.

A ramp test is not required as part of formal testing procedure, the 0.5x and 1x tripping time test confirm that the RCD trip current is within spec.

You are correct that you operate the test button after carrying out the tests, not before.
 
Not quite.

You switch off all MCBs protected by it, and drop the outgoing N connection from the RCD.
Clip on to an earth connection and probes on the outgoing terminals of the RCD with firm contact pressure.
Start the test.
You can remove L and N probes between each test to reset the RCD.

A ramp test is not required as part of formal testing procedure, the 0.5x and 1x tripping time test confirm that the RCD trip current is within spec.

You are correct that you operate the test button after carrying out the tests, not before.

Thanks very much for that, I'll run through it tomorrow.
Was confused because I never touched the rcd before, except to reset and push the test button.
 
Yeah he's a bit posh alright, I've watched a lot of his stuff too- what makes me laugh is he calls RCDs - ArseyDs.:rolleyes2:

I think JW!!!!!! is a little eccentric but certainly knows his stuff. His videos on neon screwdrivers are proof on why you should never use them.
 
Check out Steve Redpath of transeuroengineering - he's gotta be the undisputed king of the flat, monotone delivery.
https://youtu.be/NTZDrRSXtTA
I'm sure he's probably good lad though, it can't be easy presenting vids. ;)

Hmmm just thinking out loud, all these YouTube blokes that are using the socket testers for testing RCDs
The common thing that links them is they're all testing boards with one RCD on them.
Would that make a difference ?
 
Check out Steve Redpath of transeuroengineering - he's gotta be the undisputed king of the flat, monotone delivery.
https://youtu.be/NTZDrRSXtTA
I'm sure he's probably good lad though, it can't be easy presenting vids. ;)

Hmmm just thinking out loud, all these YouTube blokes that are using the socket testers for testing RCDs
The common thing that links them is they're all testing boards with one RCD on them.
Would that make a difference ?

I done my C&G 2399 with Steve redpath at trans euro. He knows his stuff.
 
I done my C&G 2399 with Steve redpath at trans euro. He knows his stuff.
Ha ha it's a small world, good job I wasn't being too mean about him.
I watch a lot of yankee guitar learning vids, they tend to have a bit more razmataz about them.
I suppose lecky testing is a more serious topic, cos of the risk of death, and all that. :-)
 
Just to add my 2 cents worth.
Yes you can test RCDs at a socket.
However you are more likely to have a fail.
The resistance of the circuit conductors between the socket and the RCD will lower the amperage of the test current, which as we know is only milliamperes to begin with.
When testing RCD sockets, it usual to use the 3 pin plug lead, rather than probes.
 
The resistance of the circuit conductors between the socket and the RCD will lower the amperage of the test current,

I love it, please can you expand on this a bit more and explain exactly how this works?

There's a chap called kirchoff who would love to hear all about it!
 
I suggest you ask Kirchoff himself to explain.

It was a joke, which you clearly didn't get!

The test current will not be reduced by the resistance of the conductors. The test current is supplied by a constant current source, not a constant voltage source, so the current will be exactly what it should be.
 
If the test current produced by the tester is then subject to resistance between the tester and the RCD, what current would be detected by the RCD?
 