Piratepete

Hi Guys
Did a small job in a house - one additional socket. Then did an RCD test - x1 (240 mSec) and x5 failed miserably. did the test a couple more times. Some improvement but still failed. The RCD is an old Wylex WSES 80/2 so replacement means a new CU. Customer asked me to test it again - it passed and continued to do so! Stabilised at 106/10 mS. Asked him when he last pressed the Test button - 6 years ago!

I assume that it just got sticky from lack of use! Does this happen to modern RCDs? I must admit that though this is the first that I've tested which failed about 5 operations I've tested many which initially give high readings (though not failed) first time around.
It seems a bit crap if whether you die or not all depends on whether the householder has pressed the test button in the last 6 months!:icon13:
Pete
 
That reminds me, I haven't tested ours in the last five months... Best not stick my fingers in any sockets just yet.
 
You'll find that most homeowners won't test these RCD'S by pushing the test button, because after the first time, they realise, that they then have to go round the house resetting all the clocks on the various appliances... lol!!
 
So very true E54.

"It's in your interest". "To hell with that if it mucks up watching Crorrie"!
 
If I knew more maths Id get the joke.


J integer is in there somewhere.?

Complex nos ...never got them first time round
 
well i think theres too much emphasis on RCDs as the be all and end all.....even to the detrement of disconnection times for MCBs.....i think we rely too much on em above all else....they still have a way to go yet....
 
I have to say that at least 1 in 5 of the RCD's I have tested over the last year (existing ones - not new installs) have failed. The majority of these have been newer ones as well - i.e. less than 5 years old.
 
I have to say that at least 1 in 5 of the RCD's I have tested over the last year (existing ones - not new installs) have failed. The majority of these have been newer ones as well - i.e. less than 5 years old.

I had 4 new out of 15 that didn't work......
Shall I disclose the manufacturer?? LOL
 
I do mainly commercial PIRs n in the comments,observations 9 out of 10 times my first comment is "No evidence of RCD monthly testing being carried out as per manufactures recommendations" Even clients who have PPM in place dont have a RCD test listed
 
The old wylex ones are pretty reliable, I buy a few from Ebay from time to time so I dont have to change old CUs just because one item has gone. 4 out of 5 turn out to be in good working order.
 
Mine at home gets regularly tested with Mrs P&S cooking exploits, however its fair to say they are variable when in situ. 3 months or so ago came across a QOE board that had 3 RCBOs, tested them and all failed. Realised the place had been un-occupied for a while and there was evidence of dampness so gave the mechanism a couple of workings by hand and tested again, still no joy. Now i knew if i could not get these working it was goodnight board but still could not get them in tolerance, with one refusing point blank to trip at all. Anyway on my last attempt one blew up in my face, which was just the time for me to condemn the whole board, go for a coffee and a smoke.
BTW i have a load of QOE breakers if anyone needs some :-)
 
At school we were taught to do the x.5, x1 and x 5 tests before the functional (red button) test as the object is not to try and get the thing to work for the purposes of testing but to test it's operation as it is, the thinking being if it misbehaves once, what is to stop it misbehaving again after you have left. We were told in no uncertain times that a first time fail is a fail, no argument, and the unit should be replaced
 
Fair point, but from my experience the second trip and subsequent re often better than the first, so rather than condemn what could be the whole board for a first trip failure, i test it to MY satisfaction
 
I generally trust em and never seen a newish one fail. I think its good that newly wired houses are usually 100% RCD protected. Cant see any downside of them apart from minor cost implication and occasional inconvenience. Its not as if they are replacing MCB's, its just additional protection.
 