Discuss Why does my current clamp meter show large current in gas pipe? in the UK Electrical Forum area at ElectriciansForums.net

Assuming both Main protective Bonding connections are in place, and your confirmation that Ze is good, I cant see there is a lot you can do.
Its always possible its originating from a neighbouring property with a fault maybe?
I watch this thread with interest.
I'm guessing it originates outside this property, as the current was there with the main switch off.
Maybe I should recommend the customer gets in touch with the DNO.
 
I read about this somewhere before. IIRC it's to do with it being TNC-S.

Your neutral back to the transformer is shared with your neighbour. Your neutral is also connected to the gas pipe via bonding. Your gas pipe is shared with your neighbour, who also has it connected to neutral via bonding. So you have in effect 2 conductors in parallel, the neutral, and the loop bypassing part of the neutral via bonding + gas pipe.

Some current making its way home will flow through the gas pipe + bonding. That's kinda what i read, anyway
 
I would report it. This could cause issues if anyone ever disconnects that gas pipe to replace the meter etc. Wonder what potential difference you would get between the two sections once disconnected?
 
Wonder what potential difference you would get between the two sections once disconnected?
I don't know. I measured the disconnected ends of the bonding and earth cables to neutral, but of course the neutral is connected to the supply main earth, so without a reference earth, I got 0 volts.
 
I would report it. This could cause issues if anyone ever disconnects that gas pipe to replace the meter etc. Wonder what potential difference you would get between the two sections once disconnected?
get a wet-pants to hold both ends. estimate the effect by the dB level of the scream.
 
I have 2 theories

1 supply is tncs I believe

If the combined neutral and earth cable is broken between transformer and some properties the following could happen.
N current from properties downstream of fault can’t flow to transformer directly.
They will then try and find an alternative path, this could be through all customers earth terminals and flowing to real earth via metal pipework buried in the ground.
The 3A you are measuring could be a small part of a huge current with multiple paths via many houses.

Or

2 an underground cable fault is raising the ground voltage around a section of the gas pipe, this is being held at close to zero volts as the pipe is bonded to earth at many houses, however the current would be shared amongst many so you don’t see a voltage rise when disconnecting main earth cable.

I think either scenario would warrant a call from the dno to check it out.
 
Reminds me of one a DNO guy told me recently, homeowner got a plumber out because she was getting very warm water from the cold tap, plumber confirmed that the cold feed was bringing warm water into the house and called United Utilities who then got ENWL involved, it was found that a faulty cable joint in the street adjacent to the water pipe was the cause of the problem
It did make wonder what an electrician would have found in the property
 

Reply to Why does my current clamp meter show large current in gas pipe? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K
Hi has anybody come across current up to 3 amps showing on water bond? 0 volts, no amps on main earth just water bond? I put a clamp Meyer to check...
Replies
7
Views
883
Just had a boiler put in on a grant scheme. Water main earth bonding was connected in with the existing gas bonding's pipe clamp on the outlet...
Replies
20
Views
6K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock