Went to a house this morning to locate a fault causing the RCD in a split load board to trip.
Going through the usual tests, I decided to put my earth leakage clamp meter on the earthing conductor.
Here is where it gets weird: with the main switch in the off position, the meter was reading nearly 3 amps through the earthing conductor!!!
So I decided for a giggle to put the clamp around a nearby gas pipe, and got around 1.7 amps through the gas pipe!!!
Ze was 0.30 ohms on what appears to be a TNC-S. Polarity is fine.
Can anyone explain this please?

20210303_114105.jpg
 
Think more outside the box (assuming the clamp meter is correctly calibrated and not low on battery) fault currents may not be from within the property but using the local gas mains as a route to the good earthing of the property, there may be a fault locally in ground around the property, this may have no relationship to the property electrics at all but regardless this can be very dangerous situation especially to other tradespeople like plumbers who may alter the pipe work and expose themselves to deadly currents.
 
Incidentally, in case anyone was wondering, I traced the RCD tripping fault to a dodgy cable in the upstairs sockets circuit. Nothing to do with my question about the current flow in the gas pipe.
 
Last edited:
Incidentally, in case anyone was wondering, I traced the RCD tripping fault to a dodgy cable in the upstairs sockets circuit. Nothing to do with my question about the current flow in the had pipe.
so did you check the current in the gas pipe/MEC after fixing the fault?
 
Think more outside the box (assuming the clamp meter is correctly calibrated and not low on battery) fault currents may not be from within the property but using the local gas mains as a route to the good earthing of the property, there may be a fault locally in ground around the property, this may have no relationship to the property electrics at all but regardless this can be very dangerous situation especially to other tradespeople like plumbers who may alter the pipe work and expose themselves to deadly currents.
Yes this what I concluded.
I disconnected the main earth and tested for voltage between the main earth and neutral- 0 volts. Tested between gas pipe and neutral- 0 volts.

Not sure what I should to go about making this safe...
 
Assuming both Main protective Bonding connections are in place, and your confirmation that Ze is good, I cant see there is a lot you can do.
Its always possible its originating from a neighbouring property with a fault maybe?
I watch this thread with interest.
 

Reply to Why does my current clamp meter show large current in gas pipe? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K
Hi has anybody come across current up to 3 amps showing on water bond? 0 volts, no amps on main earth just water bond? I put a clamp Meyer to check...
Replies
7
Views
884
Just had a boiler put in on a grant scheme. Water main earth bonding was connected in with the existing gas bonding's pipe clamp on the outlet...
Replies
20
Views
6K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
So a customer had a nuisance trip and I spent 4 hours trying to find the fault (first hour identifying circuits as none labelled at board). There...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock