Hi all,

Can someone help me please. I am trying to wire up a 2 smoke alarms to the lighting circuit. I can't wire to the light fitting as there is no constant live so need to add to the switch.

I have connected to the switch which gives power to the alarms but as the switch is a 2way for hallway and landing lights, the upstairs light stays on and just dims when switched off. If I disconnect the neutral the light works fine but then the alarms don't have power.
 
A few pics are probably going to help.
 
  • Like
Reactions: UNG
Depending on how the 2 way circuit is wired there may not be a permanant live at the switch you have chosen to connect to
 
I don’t think you’ve got a neutral at your switch.
 
  • Like
Reactions: DPG
As others above, I think you've probably got Red Yellow and Blue conductors at the switch and incorrectly assumed Blue to be Neutral which of course it isn't on a 2way circuit.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South Wales

Thread Information

Title
Wiring Smoke Alarm to Switch
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
4

Thread Tags

Tags Tags
switch

Advert

Thread statistics

Created
Rob Thomas,
Last reply from
DefyG,
Replies
4
Views
281

Advert