ab1978

hi
i'm doing the wiring for a s plan system with the boiler being a worcestor bosch combi, Problem is i can't see a switch live on the boiler to feed the honeywell junction box terminal 8 to the m/valves. The instructions show only a switch live which is used for a room stat which has a link in. do i use that? done s plans before but not using a combi as the boiler. has anyone got any wiring diagrams please?
regards ab1978
 
Yes, you can use the roomstat terminals to supply the wiring centre. Terminals 3, 4 & 5 or Ls, Lr & n.

Just check the current rating of these terminals to make sure they're happy with the loading.

Also check the boiler instructions, as it may need to control the pump directly

Alternatively you could supply the boiler via the wiring centre if there is a spur in the airing cupboard or wherever the valves etc are.

Are there multiple heating zones on this install as HW is on demand from a combi???
 
Last edited by a moderator:
hi
thanks for the reply, its only 2 2 port valves one for hot water and one for heating. is the wiring set up the same as all s plan even if its a combi boiler? i,ve gone from the fuse spur to the wiring center, then from boiler i,ve used 4 core L N permanent from the wiring center then the one left should be the switch feed to terminal 10 which is to motor/valves orange. its just where in the boiler do i connect this. looked in the instructions and the switch feed which is marked for a room stat has a link in as my room stat is wired from the wiring center.
 
Bit confused by your set up now TBH.

Is there a water storage cylinder there???


HW derived from a combi is supplied on demand I.e when you open a tap the boiler fires & heats the water.
 
yes sorry forgot to put down hot water cylinder and tank stat

And it's definitely a combi??? cant understand that at all.

The plumber must have had to mess about with the pipework a bit then + the additional cost. very strange.


As far as connecting up goes, the call signal from the wiring centre (valve orange cores) connects to either terminal 4 or Lr whichever is there, with the link removed.
 
yes your right with the pipe work its because it has 4 on suites and 1 bathroom. the combi will feed 2 of them from boiler the other 3 will come from hot water cylinder gravity feed. thanks for help i,ll have a look tomorrow and see what i can do.
 
yes your right with the pipe work its because it has 4 on suites and 1 bathroom. the combi will feed 2 of them from boiler the other 3 will come from hot water cylinder gravity feed. thanks for help i,ll have a look tomorrow and see what i can do.

Cool.

The more info you give in your first post the easier it is for us to help.:D
 

Reply to worcestor bosch combi boiler and s plan system in the Central Heating Systems area at ElectriciansForums.net

Similar threads

I have just looked at the wiring diagram on line and there are a lot of internal links which if in the wrong terminal could put 230 volt onto...
Replies
10
Views
750

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top