Making the PIR SL live from another source is not a problem while PL remains live, which is the normal state of things when multiple PIRs are wired in parallel. The unpredictable backfeeding only occurs when SL is made live from another source and PL is cut off while the PIR output is on. At that point the PIR output relay is closed and PL remains live by being back-fed from SL, so the PIR electronics stay powered. Only once all PIRs are inactive will the PL lose its last feed, de-powering the PIR electronics and releasing the latch-up condition. If the PIR has a triac output, the effects are unpredictable because the triac is then conducting in the wrong quadrants and may or may not actually hold, but there is still no true disconnection of the PL to instigate the emergency test.
We had a similar thread recently about motorised central heating valves, in which the proving contact must be fed from a separate PL that is not associated with its control input, to prevent exactly the same backfeeding situation occurring.