I have noted more and more items ask for a type A RCD rather than type AC, with electric car charging units it is often even better than type A required, but with car charging units it is hard wired so clearly should be part of the inspection and looking up one make of charger unit not really a problem.
But what about items that plug in and also smaller items like central heating boilers? I have noted that some Bosch Worcester boiler instructions state type A RCD, but to wall round a house or any other building and note what is fitted and look up each set of manufacturers installation instructions is not really practical.
And testing a RCD we remove all load so if there was some item which was causing a DC component to stop the RCD tripping we would not know, maybe part of the testing should be to check the RCD trips when all circuits connected?
It is if you like an extension of the old question, is it part of inspection and testing of in service electrical equipment or the electrical installation condition report, the whole idea is one or the other should highlight faults, but in the way some thing has degraded over time and faulty installation methods, if we assume who ever installed it did it right, why do we check for earth sleeving?
I think most car charging points will be fitted by some one who understands what is required, but smaller electric vehicles like an electric bike, or mobility scooter, clearly are still electric vehicles but the charger simply plugs in.
My own house had a new consumer unit last year, when I looked at it every RCBO was type AC, I looked on the manufacturers web site and only the 6A were available as type A. So to get a type A for over 6A it would need a new consumer unit, and it is less than 6 months old.
I am not even sure if a mixture of type A and type AC would work, as would not the DC stop other RCBO's in the same board from working?
But what about items that plug in and also smaller items like central heating boilers? I have noted that some Bosch Worcester boiler instructions state type A RCD, but to wall round a house or any other building and note what is fitted and look up each set of manufacturers installation instructions is not really practical.
And testing a RCD we remove all load so if there was some item which was causing a DC component to stop the RCD tripping we would not know, maybe part of the testing should be to check the RCD trips when all circuits connected?
It is if you like an extension of the old question, is it part of inspection and testing of in service electrical equipment or the electrical installation condition report, the whole idea is one or the other should highlight faults, but in the way some thing has degraded over time and faulty installation methods, if we assume who ever installed it did it right, why do we check for earth sleeving?
I think most car charging points will be fitted by some one who understands what is required, but smaller electric vehicles like an electric bike, or mobility scooter, clearly are still electric vehicles but the charger simply plugs in.
My own house had a new consumer unit last year, when I looked at it every RCBO was type AC, I looked on the manufacturers web site and only the 6A were available as type A. So to get a type A for over 6A it would need a new consumer unit, and it is less than 6 months old.
I am not even sure if a mixture of type A and type AC would work, as would not the DC stop other RCBO's in the same board from working?