Discuss Zdb before dead tests. in the UK Electrical Forum area at ElectriciansForums.net
swaley
Hi guys got my assesment in 3 weeks and want to get my testing spot on. Little confused whether to test Zdb on 2 way CU before dead tests?? Or do I jump straight into continuity? Thanks in advance.
Test procedures as per BS 7671 would be my choice. Would be interesting to know your reasons for wanting to test Zdb prior to dead testing.
I suppose that would depend on whether the OP is using an existing supply or not. Its not clear. I suspect he means dead testing the circuits on the sub DB
Dead tests should always be done first before live tests for safety purposes.
As you are not being inspected on safety, personally I would not worry to much. However if you want to donit by the book then dead tests first.
Thanks I'm constantly over thinking everything. I will just follow OSG in future.
Yes. Why you ask?
That wasn't clear from the op.
So I would install and test the sub main first, including live tests...
Then move on to the dead and live live tests in the new building.
You need the ze + R1 +R2 of the sub main top check the Zs of the sub main (which is also the zbd)
Then you have the zbd +R1 +R2 and then the Zs ....
So one EIC, 2 schedules ....
Where is the RCD?
Technically there is no such thing as Zdb the measurement at your two way CU is Zs. Try to use the correct terminology.
But widely used
I agree but not a abbreviation I ever quote. I believe it has been adopted where a true value of Ze cannot be established due to operational restrictions and the value is often referred to as Zdb which although often quoted is not a recognised abbreviation.
I have always taken Zdb as the measured EFLI at a DB to avoid confusion between Ze and Zs.
Ze would always Be Ze whether tested with the main earth disconnected or with parallel paths in place.
Although not a recognised abbreviation I've found it can save a lot of confusion. Especially handy when dealing with several DBs in an installation. If there was only one DB then there would only be Ze and Zs.
Yes I know that I was just wondering in what context if any it would be used in a technical report/document. My initial comment on it being the OP shouldn't really use a non recognised abbreviation on an assessment.
Reply to Zdb before dead tests. in the UK Electrical Forum area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Hi, firstly appologies if my terminology is wrong but I know very little about electrics and have no idea why this is happening - I have 2...
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...