We have Regulation 542.1.3.3:
“Where a number of installations have separate earthing arrangements, any protective conductors common to any of these installations shall either be capable of carrying the maximum fault current likely to flow through them or be earthed within one installation only and insulated from the earthing arrangements of any other installation.

In the latter circumstances, if the protective conductor forms part of a cable, the protective conductor shall be earthed only in the installation containing the associated protective device.”

The last sentence of this Regulation indicates that one installation can supply another.
 
2 installations may have a common supply as it where say at the cut out however one installation feeding as you say another is just one installation as in a supply feeding a external building fed from one consumer unit whether you TT the other end or not.
2 Consumer units fed from one cut out such as a split load DB and say a 2 way shower DB , tails in Henley blocks maybe considered 2 installations by some.

Some consider one supply equals one electrical installation regardless.
 
Last edited:
If however you wish to produce two separate EICs or EICRs, or record Ze for both installations on the one EIC or EICR, that’s totally up to you.

I use Easy Cert for all my certificates. The software allows the user to add an unlimited number of additional distribution boards to the certificate along with additional test schedules. So, if, for example, I'm testing a domestic installation that comprises of a consumer unit located at the source of the installation which in turn supplies a second consumer unit located in a garage, I would simply record the test results obtained from each board on two separate pages of the same EICR/EIC with the location and functionality of each board clearly stated. Works for me!
 
2 installations may have a common supply as it where say at the cut out however one installation feeding as you say another is just one installation as in a supply feeding a external building fed from one consumer unit whether you TT the other end or not.
2 Consumer units fed from one cut out such as a split load DB and say a 2 way shower DB , tails in Henley blocks maybe considered 2 installations by some.

Some consider one supply equals one electrical installation regardless.
I refer you again to the last sentence of 542.1.3.3.
Seems to me, to exactly describe a TT’d shed.

One problem with treating the two installations as one, is compliance with 542.4.1:
“In every installation a main earthing terminal shall be provided to connect the following to the earthing conductor:
(i) The circuit protective conductors
(ii) The protective bonding conductors
(iii) Functional earthing conductors (if required)
(iv) Lightning protection system bonding conductor, if any (see Regulation 411.3.1.2).

No mention of two METs, one for the house and the other for the shed?
 

Reply to Zdb before dead tests. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
874
Hi, firstly appologies if my terminology is wrong but I know very little about electrics and have no idea why this is happening - I have 2...
Replies
4
Views
401
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock