Discuss Ze in the UK Electrical Forum area at ElectriciansForums.net
Ross1
hi all, I posted about this recently and didn't manage to get back online till now.
I've got a Fluke 1653b multi function meter. In the last few weeks it has stopped recording Ze and Zdb readings ( readings on L-E setting) are 0.00 and on L-N reading are0.00 and PFC is 10kA ( this only happens on tncs and tns systems)
I've noticed that the Zs readings can vary quite a lot if taken at a socket outlet etc. Within seconds of testing it.
It was last calibrated in June. Do you think it's a fault with the tester or are the leads on their way out. Changed batteries.
Anyone experienced this before, I need my tester pretty much daily, how can I sort this out asap.
Cheers
Try a new set of leads? If your current leads are fused (as they should be), take the fuses out and clean the ends of the fuses. If possible clean the contacts that touch the fuses and any others in the leads. Dodgy leads can upset the zeroing process.
I did post an answer to your previous thread about this... this is what I wrote:
This might sound daft but is it possible that you have nulled the leads with bad contact at the probes or nulled one set of leads and are now using another, so that the stored offset is too high? The 1653 saves the null and uses it on continuity and loop impedance tests until you change it. Then when you take a reading it will subtract too much and possibly hit zero every time on low Zs and low continuity readings.
I don't know what it does if measurement minus null is less than zero - one would hope it would show a negative figure to indicate an invalid null but I know at least one old model of tester that didn't, so it still gave a sensible-looking zero with the probes held together leading you to assume that the null is correct.
Reply to Ze in the UK Electrical Forum area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
I hope someone can help me as im getting different answers off different people 3P & N Supply Ze: Disconnect main earth Set tester to 2 lead...
7K